    I have installed a subpanel in the garage , run 3 cond. 6AWG wire , one cond is black
    What wires get attached to main lugs in breaker box ? One is black , one is black / white , one is black / red .
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Oct 10, 2013, 06:02 PM
    One is black , one is black / white , one is black / red .
    Doesn't make sense.

    You should have black, red, white and ground.
    The black and red are your hots.

    I have to say though, someone installing a subpanel, and asking this question, should really get some on site professional help. This is about as basic as it gets and this is a pretty advanced project.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Oct 11, 2013, 10:41 AM
    Help us a little, please/

    The cable has two ends. One will connect to the main service panel and the other end connects to the downstream panelboard, correct.

    1) You must use a 4 conductor cable, not 4 conductor cable. You need to have 2 hot conductors (Black and Red), one Neutral (White or Black with 3 white stripes) and a bare or insulated equipment grounding conductor.

    On the main service panelboard a dual-pole breaker sized to protect the feeder is installed.

    On the downstream panelboard, Black will go to one pole, Red will go to the other lug. Black with white stripes will go to the Neutral bus.

    The Equipment Grounding conductor will go to the Ground bus/

    Now, is this panelboard in the same building as the main panelboard or is it in a remote building. This is critical so we can give you the proper information on the grounding and bonding of the downstream panelboard.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Air Cond. Unit Not working [ 1 Answers ]

I Have a Miller Single Package Heat Pump That I have been having some trouble with for a little while now. It started with where the fan would not cut off. By the fan being in a consent run it burnt my fan motor up. I temp installed another fan to see if I could isolate the problem. After...

Wiring cond. Fan [ 1 Answers ]

I am changing out the cond. Fan I am replacing the oem with a unv. I have speed wire and 2 comp. wires. Then I have two wires to the fan motor . The old motor had 3 wires total. My do in need to drop the old comp wire don't I?

Air cond comes on and off 3x before staying on [ 1 Answers ]

My air conditioning unit comes on then off in about 10 seconds. It does this 3 or 4 times before coming on and staying on until the house is cooled it does work. Is there something than needs fixed?

Air cond. Setting [ 2 Answers ]

This may be a stupid ? But our air conditioner has a DRY setting and we have no idea what it is? Is it for humidity? We looked in the manual an nothing. Any help? Thanks

Heating and air cond [ 1 Answers ]

Hi everyone Why there are five wires in thermostat


View more questions Search