    Both the common and neutral wire in hallway light carrying 120 volts
    Why Would My Common Wire be Carrying 120Volts When Hooked Directly To Ground Bus In box? Only Two Rooms In The House Affected.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Oct 9, 2013, 04:16 AM
    Can you describe how you measured this? What kind of meter did you use?
    How many wires are in the hallway light? What colors are they? Did you measure the voltage on these also?

    There are some possibilities how this could happen but it would be unusual...
    Notsohandywoman's Avatar
    Notsohandywoman Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 9, 2013, 04:33 AM
    I Measured It With A Fluke Meter. There Are Two Wires, One White And One black. I Measured Both And They Are Reading 122.3 Volts Each.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Oct 9, 2013, 06:35 AM
    Good morning, Notsohandywoman,

    Depending on what you are testing and how you are testing it, there is nothing wrong with your reading.

    Remember, you are dealing with an Electrical "Circuit". What goes out, comes back. The Black (Ungrounded conductor) is the supply conductor. The White (Neutral or Return) is the "Grounded" conductor.

    If you connect a meter probe to your "Black" conductor and then the Red meter probe to the White, you will see 120 (+/-) on the meter.

    If you connect the black probe to the Neutral Bus or the Ground bus or even the metal can that your panelboard is mounted to and then test the black conductor you will get 120 volts(+/-). This is normal.

    With the black probe on any grounded surface or conductor you should see 0 Volts when testing either the White or Ground conductor of a surface. Again, this is normal.

    Now, if you are testing a White conductor to Ground and you see 120 Volts, then there is a problem. This all by itself tells you that there is a "open" situation between the Neutral on this circuit and the grounding system.

    We really need more information about what you are testing and why. What is the failure you are trying to correct.

    Just for the record, The only place that "Neutral" and Ground are allowed to be connected together is at the main service panel.

    I do not know what level of electrical experience you have, so please ask more questions and give us some more information on the failure and what you are testing for.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #5

    Oct 9, 2013, 06:54 AM
    hallway light carrying 120 volts
    How many switches control this hallway light and where are you testing. If you have two or more switches and are testing at a switch, the white wire is not a neutral (common) but is a traveler (a hot carrying current to the other switch).

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

20 Volts Neutral to Ground & 100 volts Neutral to Hot [ 1 Answers ]

My outlets that have been working fine in my new house for 12 years suddenly went dead. I checked the breaker and it was not tripped. I measured the voltage and found 100 VAC from neutral to hot. I then measured Neutral to ground and found 20 VAC and 120 VAC from Hot to ground. Some how I am...

Black to white wire problem only getting about 60 volts not 120. Red to white is 120. [ 2 Answers ]

I am having a wire problem with my hot tub. Had hot tub tech come and he said the problem is in the wiring from the house to the sub panel. He said that the Red to White is reading 120, but the Black to White is only 60. Together the Red to Black is only 180 and we need 240. What could be the...

Can I get 120 volts from a 208v 4-wire service? [ 1 Answers ]

Changing out 208v high bays to 120v LED high bays. I want to know if I can just jump off one leg of the 208v for my 120v fixture.

Stratmando, thanks I don't have 120 volts between Hot and Neutral. I have 120 volts [ 2 Answers ]

Stratmando, thanks I don't have 120 volts between Hot and Neutral. I have 120 volts between hot and ground Also have 120 volts between Neutral and ground How far in the wiring do these types of problems reach into the wall?

120 volts between utility supplied neutral and ground? [ 1 Answers ]

I'm troubling shooting the lighting and the entrance to our community and have run into a problem. I thought I was just going to replace some bulbs, maybe a ballast, but things have gotten worst quickly. Turns out that with the main circuit off I still have 120 between the neutral and ground. I...


View more questions Search