    100 amp Main 100 amp Sub
    Hi, I have 100 amp panelwith 8 unused spaces, running typical fridge, maybe 3 space heaters( 12.5 amps peak winter ), micro-wave, toster, TV computer, 120 washing machine.

    I'm thinking of installing a 100 amp 6-8 space subpanel 200 ft away, but probably only need 60 80 amps at most.

    So my question is regarding how to determine maxime number of amps to be drawn through my 100 amp panel. I know I can add togther total of all my amps and see if they total more than 100, though they may not all be used at same time.

    Can I put a 100 amp 2-pole breaker in a 100 amp panel?

    r6
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Sep 13, 2013, 08:33 AM
    First, adding the amps in the panelboard is futile. You need a load study to see what the calculated load is and if you have the required amperage for your upgrade.

    Next 200', will require a voltage drop calculation (not required by the NEC)

    In answer to your immediate question, no you cannot use a 100 amp breaker inside of a 100 amp load center. You need to find out what is the largest size breaker that the manufacturer of the load center will allow.

    Lastly, because you are feeding a multioutlet secondary panelboard, you are limited to no larger than a 80% load at the secondary panelboard.
    rr6's Avatar
    rr6 Posts: 25, Reputation: 1
    New Member
     
    #3

    Sep 13, 2013, 09:09 AM
    donf.. "First, adding the amps in the panelboard is futile. You need a load study to see what the calculated load is and if you have the required amperage for your upgrade."
    Donf, there is 7 free spaces in the 100 amp panel, and if each were 15 amp, then , in theory if they each of those circuits draw 12.5 amp at same time that would be 87 amps and at most, I would use a 80 amp 2-pole breaker.

    I redid total amp at cabin and only came to 42.5-amps( see bottom of this post ) total so probably 60 amp 2-pole is plenty big enough.

    [QUOTE]
    Next 200', will require a voltage drop calculation (not required by the NEC)[/QUOTE

    Yeah I already planning on 7.6 voltage drop and yes I know that is more than recommened 5% drop

    [QUOTE]In answer to your immediate question, no you cannot use a 100 amp breaker inside of a 100 amp load center. You need to find out what is the largest size breaker that the manufacturer of the load center will allow.[/QUOTE

    Ok, that is what I thought, just looking for confirmation of that.


    Lastly, because you are feeding a multioutlet secondary panelboard, you are limited to no larger than a 80% load at the secondary panelboard.
    I suppose the mean if 100 amp main then cannot use larger the 80 amp 2-pole breaker to subpanel since 18 amps is 80% of 100 amp panel.

    Thx, for confirmation and verification mychaning day by day plan. :--). Below is assessment for this 12 x 16 single room cabin 190 ft away from main panel
    -----

    15-amps larger window air conditioner
    .. substitute 12.5 amps for space heater in winter…

    3.5-amps tiny fridge

    4-amps lights though outdoor lights draw 1.5 amps, so may 5 amps total

    11-amps coffee maker though ours is only 8 – 9.3 amps

    9-amps for 3 computers

    H,mm that is only 42.5 amps so in theory we could get by with the 70 amp panel but the problem is it only has 2 spaces,

    so we go with 100 amp panel cause it has 6 or 8 spaces, and that way we can run separate 20 amp circuits too two different walls of cabin in case you don’t want to use the same recepatcle for heater in winter that AC uses in summer.



    r6

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size required from 200 amp main to 100 amp sub panel [ 1 Answers ]

The sub panel is located @75 feet from main panel.

Wire size for feeder for 100 amp sub panel 100 ft from main. [ 0 Answers ]

I majored in sociology, so please bear with me... I am building a 400 sq ft out building with 2 1500 watt heaters, a small kitchen including a small range, small dishwasher and fan hood. There will also be a 30 gal hot water tank, and a .1/2 hp sewage ejection pump. My calculations so far...

I have a 100 amp main panel and I want to feed a 200 amp main lug. [ 1 Answers ]

The panel I have now is a 100amp main breaker and I still want the ability to keep some of the circuits that it currently has in it. I am putting the 200amp main lug in my house and was wondering if it is safe to put a 100amp break in my main panel to feed the 200 amp main lug panel and if so...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...


View more questions Search