    600 amp service
    What size wire do I need for a 600amp /3 phase service?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Sep 5, 2013, 09:44 AM
    Assuming you are in the US, you could use one set of 1250 kCM copper or two sets of 300 kCM copper or three sets of #3/0 copper...
    The above taken from NEC Table 310.15(B)(16).
    Be aware you may need to make adjustments if you are traveling a large distance or if you are in a high ambient temperature environment or when using multiple sets of cables you install them underground.

    And you thought this was a simple question!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

400 amp or 600 amp service required [ 1 Answers ]

I am building a new all electric home. I would like to know if I need a single phase 400 amp servise or a 6oo amp service. The home is 2800 sq ft, Type of high use appliances.( 2) 120amp tankless H2O heaters. (1) 50 amp tankless H2o heater. 2 ton hvac with heat stripe, 2 1/2 ton hvac with strips,...

600 amp service with a 200 amp single pole breaker [ 0 Answers ]

I have a 600 amp GE service closet in my basement that feeds 7 other socket meters and each have there own breaker. Question is I just added a brands new 200 amp panel and new line service to a area I just converted to storefront space for a deli. So I can't find a 200 amp breaker for that closet...

What size conductor do I need with a 3 phase 600 amp service [ 1 Answers ]

I want to hook up a transfer switch via generator at my shop for when the power go's out what size conductor do I need from the switch back to the load center?

Safety regarding 600 amp (Single Phase ) service. [ 5 Answers ]

I have a Single Phase 600 amp service entering my basement below grade level and running into a CT cabinet. Above the cabinet is where the electric meter is located. I need to caulk behind the CT cabinet where the electric cables carrying the 600 amp service from the outside transformer are. Is it...

600 Amp Service And Load Center With 6 Breakers [ 4 Answers ]

I Have A Overhead Service With Single Phase 220v 600amp Going To 23 Boat Docks And A Small Club House And A Garage . I Need A All New Service Change And A Rewire To The Boat Docks . I Calculated The Dock Service Demand Load According To Nec 555-12 It Comes Out To Be 486 Amps I Have 5- 125 Amp 220v...


View more questions Search