    Hvac
    My hvac blower motor works in heat mode only not cooling, will not work with manual mode either
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Jul 23, 2013, 04:20 PM
    Not knowing what brand unit you have it is either fan relay or the control board is bad
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #3

    Jul 25, 2013, 07:05 PM
    With the little information given, I would have to suspect either a bad fan motor or fan relay. The relay could be on a board or separate. Another possibility is a bad thermostat or thermostat wiring. The 'G' terminal on the stat & the wire between it and the furnace are the source of the control for the fan in cooling & manual fan. If 24 volts is not getting back to the 'G' terminal on the furnace the fan won't run in cooling or manual fan.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hvac [ 1 Answers ]

please give me the thumb rule to calculate the cooling load of 20ft X 20ft?

Hvac [ 2 Answers ]

Only 14 volts at air handler Ruud transformer

Hvac [ 0 Answers ]

I am getting 24 volt to outdoor unit ,brand new defrost board,24 volt to red and yellow, 24 volt to red and orange but nothing out of board to contactor

Hvac [ 0 Answers ]

Can you tell me when troubleshooting hvac tech will check voltage 240 v on outside condensing unit . Then he took 1 probe and touch a ground screw and put the other probe on one side of contactor and read 120v He said he does this v to ground to insure there is voltage I am not sure what this...


View more questions Search