    AC wire to compressor
    I have forced air AC with a condenser outside. The problem is that I have no power at Y on the control board output to the condenser. Does the wall thermostat control this function? The transformer is good as it tests 24 volts at R on the control board. I already replaced the control board, and the new board also shows 0 volts at Y, just like the old board did, so I am inclined to think that the board is not the problem.

    The coil/relay contacter in the consenser housing is not hooked up, as I am replacing it with a new one. Even so, I don't see how it not being hooked up would limit the Y voltage to 0 on the control board. But I am a total rube in this area, and could be 180 wrong.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Jun 14, 2013, 05:21 PM
    If the thermostat is set for cooling & set below room temperature, you should have 24 volts ac between Y & C on the board. If you do not, remove the thermostat & jumper R & Y then check the voltage again. If you now have voltage, the thermostat is the problem.
    J Russell's Avatar
    J Russell Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 14, 2013, 07:38 PM
    I jumpered R & Y at the thermostat and had no voltage. As the thermostat tested good, do I have any possible options besides the control board?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #4

    Jun 15, 2013, 06:21 PM
    You could have a broken wire between the board & thermostat. To check, set your meter for continuity, jumper R & Y at the stat, disconnect R & Y from the board, & test for continuity between R & Y. No contiuity means a broken wire.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire help for a air compressor wall plug [ 1 Answers ]

In our lab there was an old air compressor that died years ago. We had an electrician hard wire it in to a what appears to be furnace electrical switch. The switch was activated and deactivated from a light switch on the wall. The trouble is now we wanted to wire it into a outlet box to plug in the...

How to wire an air compressor switsh? [ 0 Answers ]

I have a Pro Source 1/3 HP, 2.6 Gallon, 120V, 2.5 amp, single phase portable air compressor that my brother asked me to try and fix for him. The model is 1126C and of course he dropped it, go figure. He does not have the wiring print for this unit and the three wires from the circuit board to the...

Heat pump outdoor fan runs not compressor voltage at compressor good. New compressor [ 1 Answers ]

Have a new compressor. Just replaced fan runs compressor does not, have voltage at the compressor plug? What could stop from coming on high side and low side equal at 100psig.

Wiring AC thermostat wire from house to the outside compressor [ 4 Answers ]

I have AC carrier brand outside compressor. The cable connection from the unit to the Power shutoff box and the shutoff box itself have all been rusted. I took the electrical shutoff box apart to see how it was wired and see if I can Replace it. That's when I notice something that I thought...

Compressor wire [ 4 Answers ]

Hi I have a Ruud AC unit I'm trying to get a couple more weeks out of and me living in Florida means I can't be without AC. The purple wire from the air compressor burned off and I was wondering what wire I could use for now to replace it? Please help


View more questions Search