    greenthmb1200's Avatar
    greenthmb1200 Posts: 2, Reputation: 1
    New Member
     
    #1

    Mar 23, 2007, 07:04 PM
    220 v wiring is only giving 110v
    My dad is using 220 v wiring but it's only outputting 110. He wants to isolate the problem instead of replacing the entire length of wire. Any idea what he can use to detect where the fault is occurring? I've looked but can't find anything.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 24, 2007, 04:24 AM
    I am assuming you have access to both ends of this cable, and there are no other junction boxes in between where a splice could have failed. I also assume the circuit breaker has been tested for proper output.

    There is no instrument feasible for a DIY'er to find a break in a cable, of course this really depends on the size and length of this cable.

    There are instruments available, as shown below, that we use to find open breaks in cables. We use the Greenlee, for about $500. I never heard of the other one for $150.00, but I bet it works the same. There may be others available, but none will be too cheap, unless you can find a used one on Ebay

    Electricians use Greenlee products for many things, I don't know why, because that green paint is very expensive.

    Power Probe PPECT2000 - Electronic Short/Open Circuit Tracer - SJs Tools

    Greenlee Power Finder Open Circuit Tracer, Greenlee Textron, Circuit Tracer - Mfg# 2008

    If there is some reason that replacing the cable makes it not feasible or practical, then a service call from a service electrician that has one of these units may be in order. Course, the break will need to be accessible to repair the cable.

    Really depends on the size, length, and accessibility of the cable the best way to handle this.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Mar 24, 2007, 07:16 PM
    You maybe making a mistake so basic tkrussel doesn't realize anybody would do it. You are measuring the voltage hot to hot? Each hot will only be 110 above neutral or ground. You have each hot connected to a separate pole of a double pole breaker? People have bought tandem breakers which give two 110 circuits off the same leg of the box. You need a double pole breaker which has 2 contacts one to connect to each leg.

    I would think a broken wire or bad splice would give 0 volts. There is a DIY priced tool that can find broken wires in exposed romex. I came across the niftiest gadget for trouble shooting, a voltage detector. They work through the insulation of wires. There are several brands. I have a GB Instruments GVD-505A, less than $15 at Home Depot. Touch it to a hot wire, and the end glows red. Find the doodad that lights it on one side, and not the other, and you have the culprit. You do not have to open up housings and expose electrical contacts. You are looking at where your hand is, not where the meter is. Most people are capable of doing repairs and will get it going and not get hurt if they use a little sense. The voltage detector makes it even easier.
    greenthmb1200's Avatar
    greenthmb1200 Posts: 2, Reputation: 1
    New Member
     
    #4

    Mar 24, 2007, 09:04 PM
    Thanks for both responses. I'll give them to Dad, whose having the problem. I do know that it used to run 220 so thinking it was rigged properly and hasn't been changed. But the wiring is pretty old (20+ yrs, I think). The cost involved is in replacing the entire length from the house to the dock which is about 500 ft and buried.

    Thanks again for your advice!
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Mar 25, 2007, 06:13 AM
    I am betting the wire is fine, it is a connection at one end or the other.
    pelle's Avatar
    pelle Posts: 96, Reputation: 0
    Junior Member
     
    #6

    Mar 25, 2007, 06:26 PM
    If you have the situation that labman is saying you would get no voltage reading instead of 240 when you try to read hot wire to hot wire because there is no potential difference (both hots of the same leg, same as putting your test reads on the same energized wire.

    To test this read hot to hot if you read no voltage . Read hot to ground for each hot wire if you get 120v on each one then you are wired as labman is saying. If you get it on only 1 side chances are you have a fault or even a side of a double pole breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

110 vs. 220 wiring... [ 7 Answers ]

I bought a table saw at an estate sale. I got a good deal on it! I noticed after I got the saw home (I looked at it before I bought it, but didn't look close enough) and realized the plug appears to be a 220 plug. This won't work for me as I'm limited to 110; I'm a renter. The plug has 3...

Wiring a 220 volt fan motor [ 1 Answers ]

I have a Dayton 1/3 H.P. motor Model no. 4M099C. It is a 220-230 volt motor. There are four wires coming from the motor. The purple is marked common, the black marked high, the blue marked med. And the red marked low. I want to connect these to run on 220. How do I go about connecting common and...

220 amp wiring [ 0 Answers ]

Hello... I am replacing a dryer plug (on a tanning bed), the wires are black, red, white, and a stand alone copper wire. I am unsure of where these wires go in connection of the plug... and could use a diagram

What is better to use 110V or 220V? [ 2 Answers ]

What is better to use 110V or 220V?

Wiring 220 baseboard heaters newbie [ 2 Answers ]

Hi . I am having probles setting up 2 baseboard heaters in my living room. I have the two of heaters connected and both wires going back to a thermostat box. Any help with how to connect the two heaters to a thermostat. I have a thermostat with a L1 and a t1 marked on them. I took it as L1 to main...


View more questions Search