    AAV Odors
    Hey folks. I have a very foul odor coming from under the kitchen sink. I have traced it to the AAV. I tried replacing the AAV and still have the odor. I tried blocking off where the AAV screws in with duct tape and the oder went away. Any ideas what to look now? Does the AAV have an adjustment - couldn't find one. Finally, do I really need the AAV or can I just block it off? Thanks for the help!
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    May 30, 2013, 07:37 AM
    AAV's should only admit air in and not sewer gas out. I don''t know what brand you're using but I recommend installing a Studor Vent.
    By code every fixture that has a trap MUST be vented. A working AAV Does not expel air. If you have one that does then it's faulty. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Aav [ 1 Answers ]

I have an aav that is letting water come up and out of it when I drain the sink in my kitchen. When the tap is running with the stopper out this problem does not occur. I tried pouring some drain cleaner down but this does not seem to be the problem. Why would all of the sudden, after living here...

AAV Vents [ 6 Answers ]

I have read with interest some of the questions on AAV vents for sinks/tubs. I have a problem in that I have a relatively new home 3 yrs. I do have stack vents but apparently not for the sinks. Other items toilets, tubs, kitchen and washer areas work fine. It is my two bathroom sinks that do...

Placement of AAV [ 4 Answers ]

Long story short our kitchen sink in our house needs an AAV as a result of a renovation. My question is to the exact location of the AAV downstream from the p-trap. Thank you in advance for any advice. RMH Option 1. Place it ontop of the "T" AAV L ...

How to use a AAV vent [ 2 Answers ]

In the attachement, which is the correct connection for an AAV vent. The standpipe is for a washing machine discharge. Assume the pipe is 2 inches. I assume (from prior answer) there is a desire to place vent vertically close to the p-trap (2 to 5 feet). What's the best vertical distance to...

Inline vs AAV [ 6 Answers ]

Different question same bathroom... I'm adding a washer hookup in a 2nd floor bathroom. Due to space and framing restrictions I'm not tying in to the stack on the second floor but have run 1 1/2 pvc drain down the outside wall to the basement, and joined the (vented) kitchen sink drain line...