Mar 27, 2013, 01:35 PM
|
|
Converting previous 220 compressor outlet
I currently have a 220 volt compressor outlet that I want to convert to a 4 prong outlet to connect my generator. I have the new 4 prong outlet, a new 4 prong generator cord, and a circuit breaker panel interlock kit. Question is, the current 220 compressor outlet had 3 wires, but the new plug has 4 prongs. How or can I use safely the 3 wires with the new 4 wires outlets that for my generator cables and outlet? Thanks!
|
|
 |
Ultra Member
|
|
Mar 28, 2013, 04:53 AM
|
|
Sounds like the old cable was connected to two phase conductors and ground...
You cannot use the existing three conductor cable,
You need a (4) conductor cable for connection to the supply Neutral...
|
|
 |
New Member
|
|
Mar 28, 2013, 07:17 AM
|
|
Thanks for your response.
Actually the 220 line for the compressor was run, but never hooked up. It just has the box, but no outlet was ever installed.
There are 3 wires inside the box, hooked up to a 30 Amp double pole breaker in the panel. All I would have to do is install an outlet.
My question is, since the run is currently a 3 wire (2 hot and 1 ground), how can I either convert or use the current 3 wires for a generator 4 wire plug and cable outlet? What do I do with the neutral on the plug if there isn't a 4th wire?
Thanks again!
|
|
 |
Ultra Member
|
|
Mar 28, 2013, 08:16 AM
|
|
As you have indicated the generator was designed for a (4) wire connection...
To install this properly you will need to install a fourth conductor...
You cannot do this without the neutral...
|
|
 |
New Member
|
|
Mar 28, 2013, 08:31 AM
|
|
Thanks again!
How do I install a 4th? Can I run an 8 gauge wire through the conduit? And is so, where on the circuit breaker box do I connect the 4th? I would assume a neutral bar?
What if there is weren't a neutral bar, how else could this be done?
|
|
 |
Ultra Member
|
|
Mar 28, 2013, 09:05 AM
|
|
If the overcurrent device for this generator circuit is 30 ampere, #10 awg would be fine.
... the fourth wire is most likely a neutral, so yes on the neutral bar...
If there is no neutral you do not (will not) have any 120 volt outlets..
|
|
 |
New Member
|
|
Mar 28, 2013, 09:43 AM
|
|
Thanks much! Very helpful.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Change 220 outlet to 120 outlet
[ 2 Answers ]
I have removed an old AC unit that ran off 220v and replaced it with a new unit that is 120v. It is #10 wire with black, white and bare copper. It used to be a feed to an old hot tub but when the last AC unit was installed they just used the circuit for that. When installing the new plug can I just...
Converting 110 outlet to a 220 for an electric dryer
[ 56 Answers ]
Hello,
I've recently moved into a rent house that supplies a line for a gas dryer. I have a whirlpool 3prong electric dryer that I've been using for years. Before calling an electrician I was wondering if this was a difficult task for my husband, although he is a good handy man, electricity is not...
Converting regular 3 prong electrical outlet to dryer outlet
[ 3 Answers ]
We just bought a stacking washer and dryer and now the electrical cord on the dryer won't reach down to the existing dryer outlet. Is there any way to convert a regular 3 prong outlet that is close enough into a dryer outlet?
Switch a 220 v outlet to a 120 v outlet
[ 1 Answers ]
I just got an emergency generator and it has a 220 v plug, I will not be using a 220 appliance and would like additional 120 outlets. It seems that I should be able to split the 220 into two 120 outlets. If so how to do it.
View more questions
Search
|