    Adding outlet off middle of circuit
    I have a 15amp breaker using 12 romex going to two outlets in the downstairs bathroom & then to a outlet in bathroom upstairs. I have a roll of 14 romex. "Can I use 14 romex to add a outlet for the computer on the other side of the wall running off one of the bathroom outlets?"
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #2

    Mar 27, 2013, 10:05 AM
    Yes. If bathroom has a GFI, be sure to use screws not controlled by it.

    Chuck
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #3

    Mar 27, 2013, 10:12 AM
    Well... if it's your house you can do as you wish...
    Although the code directs bathrooms circuits to be dedicated to the bathrooms
    So tapping for a receptacle in another room would not be keeping within the
    Intent of the code language...
    Bathrooms are dedicated to make available capacity for hair dryers which not only draw
    A lot of power but also create a lot of electrical noise on the branch circuit which may have some negative effect on a computer...
    If there was another circuit nearby, I would consider leaving the bathroom circuit dedicated.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Mar 27, 2013, 12:25 PM
    No, for several reasons:

    1) If the circuit serves two or more bathroom's receptacles it cab only be used for the bathroom receotcales.

    2) The circuirt is required to 20 amps. #12 AWG supports 20 amps.

    3) If you put a section of #14 AWG conductors the entire circuit must be reduced to 15 amps

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Adding a single 15 AMP outlet outside the bathroom circuit [ 2 Answers ]

Hello, I have a new house built back in 2007 in Chino, California. I confirm there is a single dedicated 15 AMP circuit that serves all three bathrooms in the house. A single GFCI outlet is the master to 4 slaves. Now I want to add a heated towel rail that is fixed on a walla and not free...

Adding outlet to 220v circuit [ 2 Answers ]

Learning as I go, so please forgive me if this is rudementary. I will explain what I need as best I can. I need to add two new outlets to an existing 10-3 wire 30 amp 220v circuit in my shop. Currently, the circuit only has one outlet on it that is in the wrong area of the shop for my needs. ...

Adding new switched outlet to existing circuit [ 4 Answers ]

I am completing a basement remodeling and am reaching the point where I'm about to install drywall. At the last minute, I realized I should add a switched outlet (both receptacles will be controlled by a single switch) at a location in my rec room. I installed the two gang boxes and ran cable...

Adding lights and outlet to existing circuit [ 1 Answers ]

I have a 20 amp circuit using 12 gauge wire. There is a total of 1000 watts of lighting on the circuit now and the "run" is approximately 65'. I want to put a single gang outlet and add about ten 25w to 40w flood lights to this circuit. My plan is to drop some conduit in a trench about 30' long...

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more questions Search