    Electrical Service
    I would like to know if it is possible to run electricity 1400 feet from a 100 amp service and have enough ampreage to run a few 100 watt lights and a well pump.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Mar 25, 2013, 09:56 AM
    The distance you want to run the cable is more then likely cost prohibitve. Not to mention the electrical design.

    For example, if all you need is 60 amp, 240 Vac, at 1400 feet, you would need a cable that supports 400 amp. That will get you 60 amps.

    You have a service of 100 amps, so your entire site would have to be re done.

    Please consider a solar source adjacent to the shed. They also are not cheap, but probably much cheeper than a 1400' run.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Mar 25, 2013, 12:04 PM
    Depending on pump size and voltage. Assuming 1 1/2 hp pump and 240v a #3 copper or #1 aluminum will probably work. Really need to know max amperage of the pump (starting amps).

    #3 copper or #1 aluminum X 1400 " = $$$$

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical service [ 3 Answers ]

This is my first shot at asking a question. Getting ready to bid on finishing a bedroom in a basement. I have several questions. This house has a 100a service. My first question is: 1. Is there a way to tell if the current 100a service has enough amperage left to cover the two circuits that...

Electrical service [ 2 Answers ]

I am a licensed electrician in North Carolina. Our inspectors are now requiring us to run sized 250kcmil al. to our 200 amp sub panel located on the interior of the house. We are feeding from a 3R, 200 amp meter combo with a 200 amp main breaker to a 225a main lug panel on the inside. The only way...

Electrical service [ 2 Answers ]

What size wire needed for 150 amp service ?

Electrical service [ 3 Answers ]

Is it mandatory to have 100 amp service in your house in order for you to be able to purchase home owners insurance

Electrical Service [ 8 Answers ]

What size service wire do I need for a 200 amp service? This would be from the meter base to the hydro incoming lines.


View more questions Search