    Submersible pump
    I installed a new pump system. The well is 400' deep and I dropped a 1 horse 5 gpm 2 wire pump. When I plugged it in to a generator it took a few minutes to get pressure. And when I opened the boiler drain at well water was just trickling out then quit. Closed the drain and no pressure built up. Also the switch never did anything. I bypassed the switch and it did the same thing; very little water. Do u think the pump is too weak to pump that high?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Mar 4, 2013, 08:53 PM
    2 wire? 120 volt pump? What depth is the pump rated 5gpm? 1 Hp @ 400 ft is pretty low especially if it is 120VAC
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Mar 4, 2013, 09:11 PM
    Brian,
    Where do you get 120V?

    1hp at 400' probably won't do it. You have to look at volume and pressure capabilities at that well depth.

    What kind of generator? You can expect about a 20% power loss for a motor on a inverter type generator.
    rtdd4's Avatar
    rtdd4 Posts: 6, Reputation: 1
    New Member
     
    #4

    Mar 5, 2013, 04:45 AM
    Quote Originally Posted by ma0641 View Post
    2 wire?? 120 volt pump? What depth is the pump rated 5gpm? 1 Hp @ 400 ft is pretty low especially if it is 120VAC
    It's 230v pump rated for 500'.
    rtdd4's Avatar
    rtdd4 Posts: 6, Reputation: 1
    New Member
     
    #5

    Mar 5, 2013, 04:51 AM
    Quote Originally Posted by hkstroud View Post
    Brian,
    Where do you get 120V?

    1hp at 400' probably won't do it. You have to look at volume and pressure capabilities at that well depth


    What kind of generator? You can expect about a 20%i power loss for a motor on a inverter type generator.
    It's a Honda 3000 230. A friend of mine has a well that is 475' and he has 3/4 horse pump. Do u think that the pump is to weak because it will only pump 5 gpm.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #6

    Mar 5, 2013, 06:01 AM
    Is the generator a Honda EU3000? Is the generator an inverter type generator?
    rtdd4's Avatar
    rtdd4 Posts: 6, Reputation: 1
    New Member
     
    #7

    Mar 5, 2013, 08:45 AM
    Quote Originally Posted by hkstroud View Post
    Is the generator a Honda EU3000? Is the generator an inverter type generator?
    Yes it is. It has me puzzled. I know everything is installed correct. The generator will kick in when u plug the pump in; then after a few minutes it idles back down. I have power to all four points on switch so I know connection is good at pump.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #8

    Mar 5, 2013, 09:02 AM
    I don't know what the amperage of the Honda 3000 output is at 240 volts.
    As stated earlier, expect a 20% loss of power of an electric motor when powered by an inverter type generator.
    A regular generator runs at a specified speed to provide a 60 cycle AC type power. It must run at that speed to provide 6o cycle power. It must do that for a large amperage load or for a small load. It produces a regular sine wave type current.

    An inverter generator can run at a slower rpm and provide 60 cycle AC power for a small load. It can do that because the generator creates AC power but not necessarily at 60 cycles. The AC power is then converted to DC power. The DC power is then converted back to AC and at 60 cycles. This is done electronically. Therefore the generator does not necessarily have to be running at a certain speed. The electronics create the 60 cycles.

    However, the voltage and amperage is not a sine wave type current. It is a square wave type current. The electric motor needs a sine wave type power. The motor will run, but at reduced power.

    Suggest you try powering pump with a different source. Either regular AC household current or a regular type generator, not an inverter type generator.

    Of course the reduce water volume and pressure would be related to the capabilities of the well it self.

    I would first try a different power source.
    rtdd4's Avatar
    rtdd4 Posts: 6, Reputation: 1
    New Member
     
    #9

    Mar 5, 2013, 09:21 AM
    Quote Originally Posted by hkstroud View Post
    I don't know what the amperage of the Honda 3000 output is at 240 volts.
    As stated earlier, expect a 20% loss of power of an electric motor when powered by an inverter type generator.
    A regular generator runs at a specified speed to provide a 60 cycle AC type power. It must run at that speed to provide 6o cycle power. It must do that for a large amperage load or for a small load. It produces a regular sine wave type current.

    An inverter generator can run at a slower rpm and provide 60 cycle AC power for a small load. It can do that because the generator creates AC power but not necessarily at 60 cycles. The AC power is then converted to DC power. The DC power is then converted back to AC and at 60 cycles. This is done electronically. Therefore the generator does not necessarily have to be running at a certain speed. The electronics create the 60 cycles.

    However, the voltage and amperage is not a sine wave type current. It is a square wave type current. The electric motor needs a sine wave type power. The motor will run, but at reduced power.

    Suggest you try powering pump with a different source. Either regular AC household current or a regular type generator, not an inverter type generator.

    Of course the reduce water volume and pressure would be related to the capabilities of the well it self.
    I would first try a different power source.

    Ok thanks for the help.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #10

    Mar 5, 2013, 02:19 PM
    Quote Originally Posted by hkstroud View Post
    Brian,
    Where do you get 120V?

    1hp at 400' probably won't do it. You have to look at volume and pressure capabilities at that well depth.

    What kind of generator? You can expect about a 20% power loss for a motor on a inverter type generator.
    He said 2 wire. Didn't note voltage.
    jlisenbe's Avatar
    jlisenbe Posts: 5,020, Reputation: 157
    Uber Member
     
    #11

    Mar 5, 2013, 05:23 PM
    He said it was 230.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Submersible pump versus jet pump [ 0 Answers ]

Which is better? I am taking water from a lake to my cottage. The distance from the lake is approx. 500 ft. Losing prime is sometimes a problem. Is it better to use a submersible pump.

Comparison between jet pump and submersible pump [ 2 Answers ]

I have a 300 feet deep bore well. Water is to be stored at 3rd floor level above ground. Which type and capacity of pump would you suggest for use?

Submersible pump runs but doesn't pump. [ 4 Answers ]

The water to my house quits periodicly. When it does this, I have tested the power to the pump and no probem. Also, I can hear the pump running but there is no pressure. I can shut the breaker off for a few seconds then turn it back on and it will pressure up normally. There is no indication of a...

Two questions pool pump & submersible well pump for irrigation in river [ 3 Answers ]

Have a inground pool about 5 yrs old that we replace motor every yr,the wireing & amount of juice is OK it's the sealed bearings that start squealing an freeze up, 2ND ? The well pump is 220v / 2 wire direct to breaker ,its on or off nothing fancy an has worked for years except this yr ,runs...


View more questions Search