    Square d pumptrol
    I have a Mc Donald shallow water 8611 pump with the square D pumptrol and the pump motor will not shut off. The right pair of contacts in the switch show considerable wear. The switch is a 30-50 and gauge is reading 30. Is the problem likely to be the switch, tube or is there a clean out in the pump head that could be clogged?
    scott53715's Avatar
    scott53715 Posts: 165, Reputation: 10
    Junior Member
     
    #2

    Feb 10, 2013, 11:25 PM
    You could have a number of problems including a new switch. See if you can measure the pressure in your pressure tank using a basic tire gauge on the air inlet (where you put air in to pressurize your tank). If the bladder in your tank is leaking, your pump will continue to try to build up pressure. Remember, if you have to replace the switch, you need to shut off the water supply and relieve the pressure by opening up a faucet. Hope this helps.
    jlisenbe's Avatar
    jlisenbe Posts: 5,020, Reputation: 157
    Uber Member
     
    #3

    Feb 11, 2013, 03:45 PM
    You have a 30/50 switch. Your gauge is showing 30# of pressure. Sure sounds like your pump is not getting up to cut out pressure. How many pipes go into your well, one or two?

    It would be wise to check your tank. There is an air valve at the top. Depress the valve center for a few seconds. Should get air, not water. If you get water, then the tank is bad.
    rlcndgo's Avatar
    rlcndgo Posts: 2, Reputation: 1
    New Member
     
    #4

    Feb 11, 2013, 11:39 PM
    Thanks for the tips. I have verified tank bladder pressure at 25 lbs, and have checked to verify that nozzle/jet opening is not clogged in pump head. I have new switch on the way and the contacts on the current one look pretty worn down. I'll let you know if pump switch is the fix. Correct pump number is 8111 (not 8611) and is it likely the venturi or nozzle need replacing? I should also add that this is a booster pump for low city water pressure and it is mounted at same level as incoming water supply.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Pumptrol square D removal [ 1 Answers ]

Removal Since this is a elecro/ mechanical pressure switch, I must first cut off the breaker, verify with a volt meter for reassurence, and then release the water pressure by simply letting the water run prior to switch removal?

Adjusting psi on Square D Pumptrol switch [ 1 Answers ]

My irrigation system requires the well pump psi to be set above 30 psi on the low end or else it drains the well. Once I cut the power and remove the cover to the Pumptrol switch, I turned down (clockwise) the center spring loaded screw down (the higher one upon which the cover was affixed). That...

Square D pumptrol [ 1 Answers ]

I have an air compressor with a square d pumptrol pressure regulator. The compressor stops at 100psi, and restarts at 60psi. How do i adjust the pressure regulator to restart at approx 80psi, without changing the shutoff press?

Square d pumptrol box shutting off [ 1 Answers ]

While watering my garden or lawn my pumptrol box shuts off... and I have to push contacts together due to complete loss in water pressure. Pump comes back on and water pressure is right there so I know I am not running out of water and I checked blatter tank for air pressure... tank was full with...


View more questions Search