    Pressure switch problem in furnace
    Please help.. I've looked at other forums but still can't find the answer. I'm getting a pressure switch error and I have done a few things already..
    1. Took the tubing off going from inducer to switch and sucked the side going to the switch.. It sucks freely for a short period then closes up with a clicking sound.
    2. Sucked the end going to the inducer and there is no airflow at all. Inducer off
    3.dettached the exhaust and found excellent airflow with no blockage.
    4. Replaced switch

    Still reading the same error that pressure switch tried 5 times and heat won't come on
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Feb 1, 2013, 04:51 PM
    Take the hose off the inducer & use a nail, drill bit, or stiff piece of wire to clean out the hole in the nipple to which which the hose connects. The "tool" should go in the depth of the nipple plus at least 1/2".
    Dguidry12's Avatar
    Dguidry12 Posts: 5, Reputation: 1
    New Member
     
    #3

    Feb 1, 2013, 06:42 PM
    Quote Originally Posted by Grady White View Post
    Take the hose off the inducer & use a nail, drill bit, or stiff piece of wire to clean out the hole in the nipple to which which the hose connects. The "tool" should go in the depth of the nipple plus at least 1/2".
    is it supposed to be free flowing air with the inducer off?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #4

    Feb 1, 2013, 07:10 PM
    Quote Originally Posted by Dguidry12 View Post
    is it supposed to be free flowing air with the inducer off?
    Yes
    Dguidry12's Avatar
    Dguidry12 Posts: 5, Reputation: 1
    New Member
     
    #5

    Feb 1, 2013, 07:11 PM
    Quote Originally Posted by Grady White View Post
    Yes
    Ok

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Problem with the pressure switch on miller furnace [ 1 Answers ]

I have a model M1B077A-Aw Miller furnace that is telling me through an indicator light that the pressure switch is open.I'm guessing that this will cause the unit to not turn on.How do I solve this issue,just short of replacing the pressure switch completely?

Pressure switch problem [ 1 Answers ]

Switch kicks on at 30 and off at 50 like it is set to but water runs for 2 minutes or so then water stops and have to wait 10 to 15 minutes usually for pressure gage to drop to 30 and kick pressure switch in builds back to 50 kicks switch off like it should water continues to run for about 2...

Gibson / Nordyne furnace reporting pressure switch problem, but no help [ 0 Answers ]

Furnace flashes 2 red blinks on mother board telling me it's a pressure switch.tried new pressure switch no help.furnace starts sequence blinks 2 flashes then will finally ignite sometimes after 3 to 5 minutes.tried cleaning out intake and exhaust tried cleaning out j-pipe bye fan motor looking for...

My gas furnace is not getting vacuum pressure for the pressure switch. [ 1 Answers ]

All the hoses were replaced as well as the pressure switch it self. I can jump it and it fires right up. It's a Heil model. The pilot light lights automatic. If you take the hose off that goes to the pressure switch and suck on it, it switches and the pilot light lights off. I don't know much...

York residential furnace pressure switch problem code stuck switch [ 1 Answers ]

I have a york furnace P2MD12H06401A after 1 hour it shuts down and gives a 2 flash error for a stuck pressure switch. The switch is new can it be wired wrong? The old one had 2 white wires piggy back and 1 blue wire. The new switch has 3 separate terminals


View more questions Search