    Garage heater hookup
    Hi,

    I have a new Dimplex EMC-4240 240V, 4,800 watt, 30 amp portable garage heater with a NEMA 6-30 (3 prong) plug at the end of a 6' cord. However the receptacle in my garage is a 2 phase, 3 pole, 14-50 receptacle, formerly used for a garage oven. The instructions advise against use of adaptors or extension cords so to use the heater safely I must replace the existing 14-50 receptacle with a one phase, 2 pole, 6-30 receptacle.

    My thought as to how to do this is: 1) switch off power to the receptacle at the main breaker panel and test to ensure all conductors are dead, 2) disconnect the existing 14-50 receptacle, 3) connect the bare/green wire to the ground connection on the 6-30 receptacle and the hot black and red wires to the other two connections, and terminate the unused neutral white wire with a marette, inside the box.

    Would this be the correct approach?

    Do I also need to change the current 40 amp breaker switch for a 30 amp breaker switch?

    Any informed advice would be much appreciated.
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #2

    Jan 30, 2013, 06:19 PM
    There isn't a "2 phase" electrical service. There are three(sometimes four) wires. One pole is 120, the other is 120 , a neutral and now an equipment ground.
    The "unused white neutral" should be connected to the same terminal as the ground (green). The breaker needs to be reduced to 30 amps. If you are not sure how to do this, to err on the side of caution, pay an electrician to do it for you. I have done a lot of electrical work in the last 40 years,, it's only friendly if you KNOW WHAT YOU ARE DOING!! Good Luck.

    Never refer to a breaker as a "switch". They are not designed to be used as switches.
    Merlan's Avatar
    Merlan Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 30, 2013, 06:54 PM
    Quote Originally Posted by Handyman2007 View Post
    There isn't a "2 phase" electrical service. There are three(sometimes four) wires. One pole is 120, the other is 120 , a neutral and now an equipment ground.
    The "unused white neutral" should be connected to the same terminal as the ground (green). The breaker needs to be reduced to 30 amps. If you are not sure how to do this, to err on the side of caution, pay an electrician to do it for you. I have done a lot of electrical work in the last 40 years,,,,,it's only friendly if you KNOW WHAT YOU ARE DOING!!! Good Luck.

    Never refer to a breaker as a "switch". They are not designed to be used as switches.
    Thanks for the answer. I stand corrected; what I meant was that the existing receptacle is wired to provide both 120V and 240V supply (for the former oven). My reference to 2 phase was wrong. I have two hot 120V wires, a neutral and a ground.

    (I will also stop referring to breakers as switches! I do use them only for the purpose they are intended but thanks again for the advice.)
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #4

    Jan 30, 2013, 06:57 PM
    That's OK Guy... just glad you walked away knowing and understanding a little bit more. THat is the great thing about life,, we can always learn something new! Good Luck

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to hookup thermo swtich wires on water heater [ 2 Answers ]

I'm installing a thermostat on my whirlpool water heater and I'm not sure where the thermo switch wires go.

Hookup a small Lp tank to main water heater [ 1 Answers ]

In an emergency, can you put a smaller tank 20LB and hook a regulator into the supply line to your home LP water heater, does this call for a high or low pressure regulator, Any additional info? Thank you, denlyn

Dual gas heater hookup [ 1 Answers ]

Where can I find a diagrahm of how to hook-up dual hot water heaters,parts required, from tank to heater

Vent free gas heater hookup [ 1 Answers ]

Hi, I have 2 charmglow 10,000 BTU I want to install in my bedrooms.They both have existing lines.The line in my room is situated strangely in the closet,but I assume the Closet were not built until much later being it is an older house.The line has a cap on it And it is close to the floor.I would...

Water heater hookup with sidearm supplimental heater [ 0 Answers ]

Hello: I'm hooking up a sidearm heater to an existing electric water heater for use with an outdoor wood furnace. I've seen diagrams showing the upper port of the potable water side hooked up to the anode port, the TPV port, and the cold water inlet port. My initial thought is that plumbing it into...


View more questions Search