Ask Experts Questions for FREE Help !
Ask
    tmjackson94's Avatar
    tmjackson94 Posts: 1, Reputation: 1
    New Member
     
    #1

    Jan 20, 2013, 06:18 PM
    Ground rod
    Can I use one ground rod for two panels on a residential duplex.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 20, 2013, 06:55 PM
    Yes, but you probably need two rods in any case.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jan 21, 2013, 05:52 AM
    The grounding is not for the two panels, should be for the Main Service, which may serve two panels.

    Check with local codes, as some states may require min of two grounding electrodes.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I ground my generator to a copper rod driven into the ground with coax cable? [ 2 Answers ]

I am going to test my 6000 watt generator. It is recommended that I ground it to a copper rod driven into the ground. I alread have a copper rod that is used to ground my telephone and cable lines. Can I use a length of coax cable to run from my generator ground to the copper rod?

Nec-covering of ground wire from the ground rod to the water pipecables [ 1 Answers ]

I installed a new service meter panel and ground rod. The ground rod is connected to the meter panel via a #4 copper wire to a water pipe located 10 feet away. Is is allowable to bury the #4 wire between the ground rod and water pipe to keep it from being a trip hazard and protect the wire? ...

Ground rod wire is not connected to the ground rod [ 1 Answers ]

My inspection report for a property that I'm looking to purchase said that my " ground rod wire is not connected to the ground rod". I have no idea what something this would cost to fix. He also said that the ground rod clamp was rotten. Am I looking at thousands in repairs?

Ground rod instead of ground wire? [ 7 Answers ]

I'd like to install an RV outlet (120v, 30amp) in our parking area. Unfortunately, I only have two wires available to that location and adding a third wire would be quite difficult. Can I use the two available wires for hot and neutral and drive in a grounding rod next to the outlet for the...

Ground Rod / ground wire [ 9 Answers ]

Hello, I am installing a 100 amp subpanel in my workshop 125' away from my house. I have two ground rods in the ground by the shop, and was wondering if it was necessary to run 4 wires from the house to the shop (two hots, one neutral, one ground), or could I just run the three wires from the...


View more questions Search