    When I test from hot to neutral I get 110v but from hot to ground it trips the breake
    I wired up a ceiling fan and it didn't work. I took the switch box apart to see which was the hot and which was the switch leg. When I tested from hot to neutral I got 110v and when I tested from hot to ground it tripped the breaker. I tested on a receptacle on a different circuit and got the same results. I don't understand. Can you help?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 16, 2013, 03:37 AM
    Would this happen to be a GFI or AFCI circuit breaker ? Either would have a "Test" button on the front of the CB. If so, what color button?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

20 Volts Neutral to Ground & 100 volts Neutral to Hot [ 1 Answers ]

My outlets that have been working fine in my new house for 12 years suddenly went dead. I checked the breaker and it was not tripped. I measured the voltage and found 100 VAC from neutral to hot. I then measured Neutral to ground and found 20 VAC and 120 VAC from Hot to ground. Some how I am...

Neutral wire is hot, black is 0v(to ground) [ 29 Answers ]

Hi guys, I'm trying to repair my three-way switch that wasn't working properly. The light would only come on if both switches were turned on, making it an "and" circuit instead of an "or". I pulled the switches out and removed the incoming power from the fuse box. I found that the neutral wire...

Wiring my hot tub neutral and ground in a 4 wire 240v situation [ 1 Answers ]

Can I run a neutral wire from my main panel bar which has both neutral (white) and bare grounds on it to 1 of 2 bars in a spa pack box containing a 50 amp gfci and 2 separate ground/neutral bars without this causing a fault and tripping my gfci? The 2nd bar in the pack I plan to use a equipment...

Receptacles hot to neutral show no volts, hot to ground show 120v [ 1 Answers ]

Replaced four receptacles in parallel, checked for loose wires. Checked the gfi breaker and 120v leaving the breaker. Tested all receptacles with voltmeter showing 120v between hot and ground, shows no voltage between hot and neutral. None of the receptacles work. Got any ideas?

"Zero" between Hot and Neutral, but Hot Neutral and Hot Hot to Ground [ 2 Answers ]

Hello! Our neighbor plugged in her vacuum yesterday. It ran for a second then shut off. All circuit breakers were set (and cycled off-on just to make sure). Troubleshooting: Hot to Neutral showed 0V. Hot to Ground showed 115V. Neutral to Ground also showed 115V.. Changed out the outlet...


View more questions Search