    70deg. Db outdoor temp.62degdb/58deg. Wb indoor temp. Suction press. 62psi, head pres
    70 deg. Db outdoor temp. 62deg db/58deg. Wb indoor temp. suction press. 65psi, head press. 195psi, evaporator temp. drop 20 deg. Compressor superheat 16 deg. Is the unit udercharge, good,overcharge
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Jan 2, 2013, 05:49 PM
    With a 20 deg drop across the evap coil, you are doing good. However, if this is a residential ac system, the inside temp may be out of range for the charts available. It really all depends on the equiptment and many other factors. Only real answer will come from an onsight professional.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My 1998 chevy venture temp gauge keeps redlining then dropping below normal temp. I h [ 1 Answers ]

My temperature gauge keeps redlining then dropping below normal operating temp. I had my thermostat replaced, still happens, flushed rad and added head gasket repair (liquid) and ran as directed heater on full. Tenp gauge stays low while driving with lots of heat but when idle at light temp gauge...

Thermostat -- reading vs. indoor temp [ 1 Answers ]

Several times I have noticed that the thermostat reads current temp as 12 degrees above what it is outside, is this right as there is nothing on at the time in my house producing heat? Is my thermostat faulty or does my house hold heat? Example temp outside 64f temp in my house 78f. I don't...

A small indoor pond (approx 30gal) room temp is 70 C. What's the water temp? [ 1 Answers ]

I'm putting goldfish in a pond and need to make sure the temp is adequate for their survival. The room is a approx 30 x50ft 20 ft ceiling. The amount of water is the only thing I'm unsure of, but it's approx 30-50 gal.

Heat not kicking on until the temp dips below 64 degrees, target temp set to 72 [ 2 Answers ]

Hello, This is my first time posting here, but I figured it was a good place to start for some advice. I just bought a new townhouse a few weeks ago and have been having some heating issues since moving in. The actual furnace (Goodman GMS 8045) was installed in June of '06 while the unit was...

Heat pump temp press? [ 2 Answers ]

I have a 2.5 nordyne heat pump at 40 deg I read 58 psi on the suction and 165 psi on the disc with a liquid temp of 90 deg register temp 88 deg.charging chart calls for 51 psi suc 164 psi disc and a liquid temp of 160 deg. 2 yr old 13 seer first season for heating. Ac mode all is fine. ...


View more questions Search