    Leaking steam radiator pipe above plaster ceiling
    My steam boiler's pressure went nuts, sent high-pressure hot water through the radiators. Now the plaster ceiling above the living room of our 1925 home is soaked and dripping water, an obvious leak in a horizontal pipe leading from one room to another. Am afraid the young plumber who came doesn't know what he is doing. He began chopping at the ceiling with the claw end of a hammer and then stopped. What is the appropriate way to access and repair this pipe?
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #2

    Jan 2, 2013, 04:49 AM
    Do you have a one pipe or two pipe system?

    Is it possible the leak is coming from a radiator above the living room?

    Have you removed the excess water from your system?

    If there is a problem with the pipe in ceiling then ceiling has to be opened to expose the pipe. From there you can determine how to repair.

    Chuck
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #3

    Jan 2, 2013, 06:23 AM
    I'm afraid of any plumber that starts hacking away at the ceiling, too! In my opinion, any job of this nature requires a drop cloth and a small attempt by the plumber to make a reasonable hole so it can be patched without too much effort.

    Personally, I have made it a standard procedure to cut all my holes nice and square in hopes that I can replace the cut out piece. I even carry some patching plaster and seam tape in the truck... nothing beats seeing my customer's face after I open the ceiling, fix the leak, place the ceiling board I took out back in place and then tape out the first plaster coat!

    With all that being said, I guess some plumbers just hack a hole to start, but see if you can get him to take an extra minute or two to square the hole up once he is done with the job... ;)

    Check out my answer to your pinhole question at your other post, OK?

    Mark

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Steam boiler is returning water via steam pipe rather than through condensate tank [ 0 Answers ]

I have a steam boiler heating system in my home. After steam is produced and goes to the radiators, it is condensating and returning to the boiler via the steam pipe rather than the pipe leading to the condensate tank. It is a two pipe system. The boiler overfills after each cycle and I have to...

Move steam radiator [ 0 Answers ]

I am renovating a bathroom which will require moving a steam radiator. It has a 1.5" galvanized pipe which I want to extend from the shutoff valve to the new location which will be 3-4 feet away. Any advice before I start? Dakota

Radiator Pipe Steam Leak [ 1 Answers ]

I originally posted this in HVAC, but was told that a plumber might be best to advise on this one. I have discovered a leak in an 80 year old steam radiator system. The pipe shown is 4" diameter cast iron that holds steam. It is below the floor and there is dirt below the pipe. It leaks at the...

Radiator Pipe Steam Leak [ 3 Answers ]

I have discovered a leak in an 80 year old steam radiator system. The pipe shown is 4" diameter cast iron that holds steam. It is below the floor and there is dirt below the pipe. It leaks at the seams where the old is attached to the new. It looks to me like someone cut out a section of the...


View more questions Search