    FMC size-3/8" or 1/2"?
    I'm installing an under eve outdoor floodlight, the standard two bulb type, going to use 150W floods. I also plan on using two switches so I can control each lamp separately. It will be wired with four #14 THHN/THWN-two hots, neautral and eqpt. Ground. The wire will be in conduit except for the last four feet where I need to use FMC. The lights will not be continuous use.

    I planned on using trade size 3/8" FMC. Table 348.22 alllows up to four wires plus a ground of the same size based on my wire selection when using fittings outside conduit. However, I know there is more to it than just fill amount.

    Based the 300W total is the 3/8" acceptable or should I use 1/2" FMC?
    PJmax's Avatar
    PJmax Posts: 70, Reputation: 3
    Junior Member
     
    #2

    Nov 18, 2012, 09:21 PM
    1/2" sealtite
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #3

    Nov 19, 2012, 05:31 AM
    1/2" flexible nonmettalic conduit would also be a good choice...it's listed for exterior
    use. I would not use flexible metal conduit for an exterior application. Most if not all outlet boxes have 1/2" openings at smallest.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 19, 2012, 07:58 AM
    3/8" FMC with outside fittings will work fine, as you propose, providing this is not a wet location.

    FMC was allowed in wet location prior to the 2008 Edition of the NEC.

    If this is a damp location, you may use FMC.
    afscme's Avatar
    afscme Posts: 23, Reputation: 4
    New Member
     
    #5

    Nov 19, 2012, 04:08 PM
    I tried to cover everything in my post, but omitted the fact that the small run of FMC will be IN the eve, not exposed to the elements, and connected to a surface mount flood--so my question is answered. Thanks for all the responses, much appreciated.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Please convert "Evolution", "Transformation", "Phoenix" in Sanskrit [ 0 Answers ]

Please convert 1. "Evolution", 2."Transformation", 3."Phoenix" in Sanskrit God bless - this will be used for a tattoo

Collector's Guild LTD, NY- "original etching" "Pour Roby" Picasso "Star Scene" J Moro [ 0 Answers ]

Both pictures have stickers on the back stating with a "certification seal" that the Picasso is a original etching and the Joan Miro is a lithograph. Moro looks real to me but I can't take the frames off to feel if the paint is real or maybe I don't know what a lithograph should feel like just a...

"Form" placed in "Microsoft Access" can be accessed from a "Button" in "VB.Net" App [ 1 Answers ]

Hi All, Actually, I'm not very well in programming but a task is assigned to me related to .Net. Basically, there is a database in Microsoft Access. I have made forms in it which are based on queries to retrieve required results. I have also made graph of it. Now, I have to merge this...


View more questions Search