    Is 3 phase required?
    I am setting up a new store and everyone keeps pushing 3 phase power, my total load with a 25% buffer is 21611 watts

    I have one machine that the manufacturer specifies as single phase 3 wire 5500wats on a dedicated 3 amp circuit and the other large machine is 3154 watts single phase on a 20 amp dual pole circuit, the rest are common fridges, lighting etc

    Is there a need or advantage to 3 phase?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 11, 2012, 04:44 AM
    I do not think 3 phase is needed for this small load. Have your electrician price the service entrance both ways. Check with the utility for billing charges for both. Compare both costs and make your decision.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Nov 11, 2012, 05:30 AM
    If you are in a mall or strip mall it may be required, other than that I highly doubt it.
    The advantage to 3-phase is it is much more efficient for motors and similar loads, like A/C units. The other advantage is you get 50% more available power.
    A down side is that many 3-phase services are 120/208V delta. This means one out of every three breaker poles is a 208V high leg that you cannot use for 120V loads. So if you have little to no 3-phase loads 1/3 of your main panel will be wasted space, and you'll likely need a sub-panel.
    Alchemy's Avatar
    Alchemy Posts: 6, Reputation: 1
    New Member
     
    #4

    Nov 11, 2012, 08:18 AM
    Quote Originally Posted by stanfortyman View Post
    If you are in a mall or strip mall it may be required, other than that I highly doubt it.
    The advantage to 3-phase is it is much more efficient for motors and similar loads, like A/C units. The other advantage is you get 50% more available power.
    A down side is that many 3-phase services are 120/208V delta. This means one out of every three breaker poles is a 208V high leg that you cannot use for 120V loads. So if you have little to no 3-phase loads 1/3 of your main panel will be wasted space, and you'll likely need a sub-panel.
    I have a couple of problems,
    The install is in an Airport in Mexico, and my spanish is limited, the specialized equipment are both heating units for cooking, but should not be operating continuously, the manufacturer specifies single phase 3 wire. It does give the option of 120/208 or 120/240 on the plate

    The original people we had do the plans made so many mistakes I was thinking that the three phase was also a mistake.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Nov 11, 2012, 08:19 AM
    Well if the equipment requires 3-phase then you have no choice.
    Alchemy's Avatar
    Alchemy Posts: 6, Reputation: 1
    New Member
     
    #6

    Nov 11, 2012, 08:21 AM
    Quote Originally Posted by stanfortyman View Post
    Well if the equipment requires 3-phase then you have no choice.
    That's my confusion, the plate specifies single phase
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Nov 11, 2012, 09:46 AM
    Just curious, but are you confusing 3 wire with 3 phase?

    "3 wire" is a description of a cable.

    "3 phase" is the description of the electrical supply to a building.
    Alchemy's Avatar
    Alchemy Posts: 6, Reputation: 1
    New Member
     
    #8

    Nov 11, 2012, 09:59 AM
    Quote Originally Posted by donf View Post
    Just curious, but are you confusing 3 wire with 3 phase?

    "3 wire" is a descripton of a cable.

    "3 phase" is the description of the electrical supply to a building.
    No, I wish it were that simple, on the chart of charges the load is balanced between the three phases
    Attached Images
     
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Nov 11, 2012, 10:16 AM
    That is quite obviously a single phase machine. Whoever suggested otherwise has no idea what they are talking about.

    By 3-wire the plate means two hots and a neutral, plus the always required equipment ground.
    Alchemy's Avatar
    Alchemy Posts: 6, Reputation: 1
    New Member
     
    #10

    Nov 11, 2012, 10:21 AM
    Quote Originally Posted by stanfortyman View Post
    That is quite obviously a single phase machine. Whoever suggested otherwise has no idea what they are talking about.

    By 3-wire the plate means two hots and a neutral, plus the always required equipment ground.
    Yes that's been my frustration

    I just reviewed a pic of the existing panel and I think I know why they are pushing 3 phase, not sure though but I think the unit is already equipped with three phase
    Attached Images
     
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #11

    Nov 11, 2012, 10:26 AM
    That definitely is a 3-phase panel, with one 3-phase branch breaker. Do you know where that goes? HVAC would be my guess.

    I have to ask, why is the feeder missing?
    Alchemy's Avatar
    Alchemy Posts: 6, Reputation: 1
    New Member
     
    #12

    Nov 11, 2012, 10:31 AM
    Quote Originally Posted by stanfortyman View Post
    That definitely is a 3-phase panel, with one 3-phase branch breaker. Do you know where that goes? HVAC would be my guess.

    I have to ask, why is the feeder missing?
    The blue wires are hvac, not sure what you mean by the feeder,

    Would connecting the equipment to 3 phase damage it?

    This explains a lot
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #13

    Nov 12, 2012, 03:49 AM
    Looks like the 3 pole 40 Amp breaker is the Main Breaker, backfeeding this 3 phase 4 wire 120/208 volt panel.

    The feeder conductors seem large, look like #2 copper. I wonder why only 40 amp feeder?

    5500 watts at 208 will draw 26 amps. An electrician needs to look at this installation and determine if the existing panel can handle the added 26 amps, plus the existing load, all on a 40 amp feeder.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #14

    Nov 12, 2012, 04:51 AM
    Looks like the 3 pole 40 Amp breaker is the Main Breaker, backfeeding this 3 phase 4 wire 120/208 volt panel.

    The feeder conductors seem large, look like #2 copper. I wonder why only 40 amp feeder?

    5500 watts at 208 will draw 26 amps. An electrician needs to look at this installation and determine if the existing panel can handle the added 26 amps, plus the existing load, all on a 40 amp feeder
    I got in late last night and read this but did not reply.
    I was thinking the same thoughts.

    And if this panel is existing what are they talking about with giving him 3-phase, it's already there. Maybe they are talking about an upgrade due to the added load?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #15

    Nov 12, 2012, 05:47 AM
    Yea, who knows, Alchemy needs to consult with an electrician that can review the system.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Three phase energy meter working principle in single phase distribution [ 1 Answers ]

What is three phase energy meter working principle in single phase distribution? If one phase have no current other two take current then how the meter calculate the energy?

Single phase phase separation for rotary phase converter [ 5 Answers ]

I have a 240V Roto-Phase converter (ARCO Electric model M) in my shop installed by an electrician. A wire came loose last week and while debugging that I started thinking about the way it was wired and confused myself. My understanding of 3 phase power is that each leg is 120 degrees out of phase...

How do I change a 3 phase electrical subpanel to two single phase panels? 5 wires [ 1 Answers ]

We have a building with two separate office suites, but only one meter and remote one sub panel. The meter and feed is 3 phase, 5 big wires to the one panel through a 2.25 inch underground conduit. There is room for another meter in the meter box in the pedestal. Can we run two meters and two...

How I know if my house use a single-phase or triple phase electric panel breaker? [ 10 Answers ]

I am trying to buy the "plug and save", but I do not know what kind of phase panel I do have... how can I check what is the one I have? Thanks!

Single phase vs. 3 phase power - what makes 3 phase more efficient? [ 1 Answers ]

Hi, What is it that makes 3 phase power more efficient? Suppose I need an air compressor for a printing shop and I can choose between a 7.5HP single phase and a 7.5HP 3 phase. Ignoring that the cost of the motor is a little less for 3 phase, why is the motor more efficient and how does...


View more questions Search