    New Bathroom Wiring
    I am installing a new bathroom in my basement. I plan on having a total of three switches (one for the vanity light and two individual ones for a combination ceiling exhaust fan/heater) and one GFI outlet.

    Summary:
    1- Light Switch
    1- Exhaust Fan Switch (timer)
    1- Heater Fan Switch (timer)
    1- GFI Receptacle

    The ceiling unit is a Panasonic (FV-11VH2). The individual supply to the fans are 120V and the heater is 1400W. The exhaust fan draws 30W.

    Am I required to provide (2) circuits - one for the GFI and one for the lights/fans or can I put them all on (1) circuit?

    Thanks!
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Oct 23, 2012, 04:29 AM
    I would recommend (2) 20 ampere circuits... one for the GFCI receptacle and the other for the fan / light / heater...
    A dedicated GFCI circuit will allow hair dryers to be used as most are large enough to require a dedicated circuit anyway.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Oct 23, 2012, 06:03 AM
    First, allow me to state that the above statement is correct.

    The NEC allows the following:
    If the only devices being served are the ones in a single bathroom, you only need one 20 amp circuit. You would have to be careful of the placement of the GFCI protection.

    Now, think about this, your wife or daughter are busy drying their hair and they have the heater on. The breaker trips and now they are in the dark. Do you really want to have a conversation with either lady at that point in time?

    The second allowance for bathroom circuits is that you may have a separate 20 amp, GFCI protected circuit that is for a receptacle only and that that branch circuit may serve other bathroom receptacles, ONLY. In which case you might be able to use a 15 Amp circuit for the light, fan and vanity light.
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #4

    Oct 24, 2012, 05:00 PM
    Ahem, The NEC does not "allow", it requires minimum standards be met. You may put as many circuits in a bathroom as you like, provided they are placed properly and GFCI protected as required.

    What about the heated floor, and the whirlpool tub ?
    Renman521's Avatar
    Renman521 Posts: 24, Reputation: 2
    New Member
     
    #5

    Oct 24, 2012, 07:12 PM
    Thanks for the answers. I plan 2 circuits so in the future I can provide power to two gfi outlets in two additional bathrooms
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Oct 25, 2012, 06:53 AM
    Shuntriper,

    I apologize for the use of the word "Allows" forgive me. However, that said, my response is accurate and does state the minium requirements as set forth in the NEC.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New bathroom wiring [ 6 Answers ]

Hi, I am wiring a new bathroom. I have the following to install: 3 recessed lights, 1 GFCI outlet, 1 Nutone exhaust fan, 2 sconce lights Can I do the following? Run 12-2 romex from a 20 amp breaker to the GFCI outlet Run 12-2 from the GFCI outlet to a 2 gang switch box Control the sconce...

Help Wiring Bathroom [ 4 Answers ]

Can anyone help me with a wiring sequence for the attached drawing. I would like to control all the ovrhead lights with one switch and the fan with another. Is there anyway to get the light from the fan/light combo on the rest of the lighting cercuit? I will have a separate switch for the vanity...

GFI bathroom wiring [ 11 Answers ]

I am in the process of remodeling an older bathroom (1965) and had a question regarding the wiring. From the single switch box where the feed from the circuit breaker comes in there is a 12/3 circuit going to the ceiling fan/light. There is also a 12/2 going to the vanity light. Can I change the...

Wiring a New Bathroom Fan [ 5 Answers ]

Need a master bedroom bathroom fan to control humidity. New install and plan to have a timer vs a switch. Have one light fixture on wall over bathroom medicine cabinet. This fixture is controlled by a switch located just outside of the bathroom and there is 1 black wire in and then 1 out, so I...

Bathroom wiring [ 1 Answers ]

I am wiring an elecric towel rail & blanket underfloor heating in a bathroom, I know this has to be done to IEE standards trough a flex outlet & an external fused connection unit. I just looking for conformation on what height I should put the flex out let in the bathroom. I am in Scotland, I...


View more questions Search