    Copper to Aluminum and Grounding
    I am trying to install a new light fixture to an older existing box. The box is copper, the fixture is aluminum. How do I attach them safely? Also I have two grounding wires coming into my box. Is that normal? Do I need to attach both of them to the grounding wire on fixture is do I need to attach them to separate things?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Oct 19, 2012, 09:32 AM
    remodelmom,
    When you say the box is copper... do you mean the wiring in the box is copper or is the box itself actually made of copper?
    As far as equipment ground conductors go all of them should be connected together along with attachment to the electrical box if it is made of metal.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Oct 19, 2012, 12:11 PM
    I have never seen a new fixture with aluminum wire. It may be plated copper that looks like aluminum. Is the fixture wire set clear or black and white? Attach all the grounds together and pigtail a ground to the metal box.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Aluminum main panel to copper sub panel with aluminum wire? [ 7 Answers ]

I am upgrading branch wires in a house from aluminum to copper. Replacing all boxes... switch/outlet/receptacle/lighting, etc.. The house currently has a main panel (or lug not sure which.. maybe lug because there is no "main" breaker) next to the meter. The main panel is aluminum rated and has...

Copper/Aluminum SEC [ 2 Answers ]

110.14 prohibits the use of conductors of dissimilar metals in the same terminal or connector unless the terminal/connector is identified as for that purpose. As a result, need some advice from the pros. The SEC on both sides of the meter are the original aluminum. I updated and relocated the...

Aluminum to Copper ? [ 2 Answers ]

Hello, My mother-in-laws house built in the late 50's has Aluminum wiring throughout. I need to run a new leg ( one-20 amp outlet) from an existing circuit, 20amp AL 12-2/g. Can I do this with copper 12-2/g or need to run new circuit from panel. Also what about GFI outlets on aluminum?

Copper vs aluminum [ 8 Answers ]

I am in the process of building a house and my electrician seems to favor using aluminun wire for some aspects of the house wiring and pushes back when I suggest copper in these instances. First the 200A underground supply cable from the meter to the panel (maybe about 70 feet). He says copper...

Aluminum or copper? [ 6 Answers ]

My husband and I recently acquired a hot tub. We would like to install every ourselves but are totally green on the subject. So, we have decided to at least purchase the materials and have an electrician just hook it up to the box. What type of wire should we buy. I know it is 6/3 but the hardware...


View more questions Search