    How do I run power to 2 separate cabins from same conduit?
    I want to run power to 2 cabins, which are going to have 60 amp in each cabin but I want to run one set of wires in one conduit then split off in between the cabins. How would I do this? Would I use a 120 amp breaker? This is the main part I'm confused about. How does it split off evenly?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 27, 2012, 06:49 AM
    The feeder would need a 125 amp breaker, assuming the feed panel has a 125 amp CB available.

    This feeder can be split at a wire trough and then into two 60 Amp disconnects.
    kboyd612's Avatar
    kboyd612 Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 30, 2012, 07:00 AM
    I'm unsure of what this wire trough is, there will be 3 conduits sticking out of the ground, one from the feed panel, and one from each cabin. I will cover them up safely later after making connections. Do I connect the ungrounded feed wire to the 2 other ungrounded wires going to the cabins directly? There is a 60 amp disconnect in each cabin. Do I run a ground wire and a grounded wire also? The cabins have their own grounding rods. I can figure out wire sizes later but if it helps with an answer the cabins are about 45 feet apart and the center of them is 120 feet from the feed panel.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 1, 2012, 04:46 AM
    How do you plan to handle the connections at the location that three conduits meet?

    A wire trough is a junction box.

    At that location is where two fusible disconnects need to be one for each cabin.

    You may be better getting an electrician on site to handle this project.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Run the GEC in same conduit with SubFeed Conductors? [ 2 Answers ]

I am backfeeding a 200 amp service with 4/0 AL XHHW conductors in a 2.5" Rigid PVC conduit to a J-Box and then continuing through the basement with SER. I would like to run the 1/0 CU GEC with my subfeed conductors through the PVC. At the J-Box, the GEC would continue to the water pipe. The water...

Minimum distance between emt conduit for data and emt conduit for power [ 1 Answers ]

Minimum distance between emt conduit for data and emt conduit for power?

I have romex installed in a conduit for about an 8ft run. Is this OK? [ 2 Answers ]

I upgraded my garage to add a couple of receptacles. The bulk of the wire is running through the rafters of my basement, but I enclosed about the last 8-10ft of romex NM-2 in 1" PVC conduit for mainly protection since this was going to be exposed. Now I have some concerns after reading that I...

Can I run a power cord conduit [ 1 Answers ]

I have a residential sewage pump station in the front of my house. It’s a 300 Gallon concrete pump chamber. In it, there is a Gould (Model 3886) Submersible sewage pump with a 220v plug that gets plugged into a SJERhombus Super Single pump switch that has a piggyback plug. That plug in turn...

Do I need conduit to run a 220v cable through my cellar? [ 10 Answers ]

I'm running a 2-2/4 aluminum cable for a 220v circuit from my barn from the panel in my house. Once entering the home (from the 36" deep in-conduit run from the barn), I have to string the cable through the mechanical area (cellar) of the house, then through a center-home crawl space and then...


View more questions Search