    My preasue on the low side is 38 the high side is 215 what is the problem
    On the low side of the unit it reads 38 degrees, the high side is 225 it should read 60 to 225 what could the problem be. I check the orphis to see if it was clogged but it showed good
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Sep 25, 2012, 04:29 PM
    So you have a piston/orifice metering and not a txv metering? Could be a number of things. Plugged filter/drier, plugged screen on inlet side of orifice would be my first guess. Low charge could also come into play, depending on the temps outside, etc, etc Lots of options here. I you are not familiar with a/c systems, its not just something that can be learned over the internet, trust me. May be time to call in a tech. If you are indeed licensed in refrigeration, and just need a little help, we may be able to help to a certain extent, but even that is hard to do without putting our actuall hands and tools to the equiptment. Let us know what you are thinking. Take care.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My goodman low side is 66 and high side is 264 is this a good #at 99 degrees [ 0 Answers ]

When I went to it the suction side was 76 and high side was 412 an climbing so I released some freon to relieve the compressor my vent readings were 47 and 53 degrees before it was 70.3 could my filter drier have been plugged

Dodge stratus air conditioning high side has low and low side has high pressure how [ 0 Answers ]

Our dodge stratus 2001 air was cooling and then not cooling then cooling again Took it to our mechanic he said he did not know how to repair. The compressor was good, but the high pressure line is now low pressure, and the low pressure has highest pressure, he said he did not know what was causing...

Unit has 160 on high side and 40 on low side will freeze up coils are clean [ 2 Answers ]

One ac company says bad evaporator, one says bad compressor. Unit has always performed well. I made sure coil;s are clean ? Seems hard to trust anyone on the repair.

Heat pump low side and high side lines both warm I have comfortmaker 13 seer [ 2 Answers ]

Both my high side and low side are reading 115 psi. High side line is warm and low side is warmer, not getting sufficient heat what could be the cause? Could it be the valve?


View more questions Search