    230v 3 wire submergable pump has only 3 wires
    My 230v 3 wire pump only has a red black and yellow wires no 4th wire green .
    Do I need it if so where do I connect it to pump
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #2

    Sep 16, 2012, 08:06 AM
    Read the motor plate, what does it say ? Single phase or 3 phase? What is the voltage on the plate? What is the amperage? Are you describing the wire coming out of the motor or the wire coming in to the motor?
    Grouchy53's Avatar
    Grouchy53 Posts: 4, Reputation: 1
    New Member
     
    #3

    Sep 16, 2012, 11:18 AM
    Quote Originally Posted by shuntripper View Post
    read the motor plate, what does it say ? single phase or 3 phase? what is the voltage on the plate? what is the amperage? are you describing the wire coming out of the motor or the wire coming in to the motor?
    230volt single phase 3wire submersable well pump 3/4 hp all wiring diagrams show 4wires mine only has 3 red black yellow mine has no green wire.
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #4

    Sep 16, 2012, 11:59 AM
    Red and yellow is the start winding wire, black and yellow is the run winding, you need a pump control box for this pump, to switch from start to run mode.
    You should have a ground wire from the well casing to the control box also

    Here's a link to a diagram, page 8 looks like your setup

    http://www.berkeleypumps.com/resources/images/2101.pdf
    Grouchy53's Avatar
    Grouchy53 Posts: 4, Reputation: 1
    New Member
     
    #5

    Sep 20, 2012, 06:42 PM
    My casing is pvc can I hook a ground wire to one of the motor to pump mounting studs? Or should I just drive a ground rod for ground?
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #6

    Sep 20, 2012, 07:06 PM
    Quote Originally Posted by Grouchy53 View Post
    My casing is pvc can i hook a ground wire to one of the motor to pump mounting studs? or should i just drive a ground rod for ground?
    Post the pump model number and manufacturer
    Grouchy53's Avatar
    Grouchy53 Posts: 4, Reputation: 1
    New Member
     
    #7

    Sep 21, 2012, 04:31 PM
    Quote Originally Posted by shuntripper View Post
    post the pump model number and manufacturer
    Franklin elect.1/3hp 230v 4.4amp 3wire pump motor model#2143034116 crane deming pump metal tag on pump reads 2xln-12-482
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #8

    Sep 22, 2012, 06:44 AM
    Looks like Franklin wants a 230v GFCI breaker feeding the well pump, the water column can become a ground path and possibly kill someone when a plastic drop pipe is used.
    That part number does not search out on their site. Is this pump submersible or is this a motor bolted to a pump above ground? The part number looks more like that situation, in that case run a ground wire same size as motor conductors to the motor make up box and ground it there.
    Here is the installation pamphlet from Franklin
    http://www.franklin-electric.com/med...IM_Catalog.pdf
    I copied this off page 9

    The primary purpose of grounding the metal drop pipe
    And/or metal well casing in an installation is safety. It is
    Done to limit the voltage between nonelectrical (exposed
    Metal) parts of the system and ground, thus minimizing
    Dangerous shock hazards. Using wire at least the size of
    The motor cable wires provides adequate current-carrying
    Capability for any ground fault that might occur. It also
    Provides a low resistance path to ground, ensuring that
    The current to ground will be large enough to trip any
    Overcurrent device designed to detect faults (such as a
    Ground fault circuit interrupter, or GFCI).

    An above ground surge arrestor must be grounded,
    Metal to metal, all the way to the lowest draw down water
    Strata for the surge arrestor to be effective. GROUNDING
    THE ARRESTOR TO THE SUPPLY GROUND OR TO
    A DRIVEN GROUND ROD PROVIDES LITTLE OR NO
    SURGE PROTECTION FOR THE MOTOR.
    To maximize delivery, are not recommended, since the
    Suction created can be lower than atmospheric pressure.
    %QUIPMENT 'ROUNDING
    Primary path back to the power supply ground for any
    Ground fault. There are conditions, however, where the
    Ground wire connection could become compromised.
    One such example would be the case where the water
    In the well is abnormally corrosive or aggressive. In this
    Example, a grounded metal drop pipe or casing would
    Then become the primary path to ground. However,
    The many installations that now use plastic drop pipes
    And/or casings require further steps to be taken for
    Safety purposes, so that the water column itself does not
    Become the conductive path to ground.
    When an installation has abnormally corrosive water
    AND the drop pipe or casing is plastic, Franklin Electric
    Recommends the use of a GFCI with a 10 mA set-point.
    In this case, the motor ground wire should be routed
    Through the current-sensing device along with the motor
    Power leads. Wired this way, the GFCI will trip only when
    A ground fault has occurred AND the motor ground wire
    Is no longer functional.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do I wire 1ph 208-230v outlet [ 4 Answers ]

Have to wire outlet for commercial freezer unit. Needs 1ph 208-230v. Plug is 15A/250V. Do I run 2 "hot" leads from same phase and one N/G to round pin? Not sure how you get 208-230 from one phase? Thanks - SM

Installing 230v 12-3 wire for irrigation 2hp mtor [ 1 Answers ]

I have a double pole 230v 20amp breaker to install in the box. I want to run it out to the lake and connect a single outlet with a switch.

I am trying to wire a 230v 50amp stick welder to my dryer plug, is this possible? [ 2 Answers ]

The welder has 4 wires black,white,red and green. The dryer plug is 3 wire. The dryer receptacle is black, red,and white.please help!!

I have a VFD input 230V 28.5A... out put 230V 10A 3phase, what breaker & wire gauge? [ 4 Answers ]

I inherited a 1972 Unisaw 3hp 3Phase motor. I have a 30 amp breaker going to my detached garage with a sub panel of 4 15amp breakers. The VFD to run the saw has an input of 230V single phase 28.5amps (I am not sure if this is the correct amount of amps, seems kind of high) and an output of 230V...

Wiring 230v welder has 2 wires and ground which one is hot? Both are same coloc [ 1 Answers ]

Just bought older welder. Instead of plug it has two black wires and a post for the ground. Welder requires 230v 60hz single phase. I have a standard 220 outlet


View more questions Search