    Outlet
    I have replaced an outlet with 4 wires. The outlet works, but the switches and outlets down the line do not. What have I got wrong?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Sep 13, 2012, 08:56 AM
    By 4 wires do you mean 2 wires entering the box from one side and 2 more exiting the other side? Are the wires just 2 black and two white, no gren or bare? With the receptacle removed only one black wire should be hot, use a tester to determine which one. Hot black goes on the yellow brass screw and white to the silver screw. There are two brass screws, the other black goes on the other brass screw. The second silver screw gets the other white wire. When finished turn the power back on and test. You should get 120 between any white and any black. Back to you for your results. When starting this work test between the black and white to insure power is actually off.
    Luther42's Avatar
    Luther42 Posts: 5, Reputation: 1
    New Member
     
    #3

    Sep 13, 2012, 09:12 AM
    Yes, two whites and two blacks plus a ground. One black is hot. I put two blacks on the brass side and two whites on silver side.
    ebaines's Avatar
    ebaines Posts: 12,131, Reputation: 1307
    Expert
     
    #4

    Sep 13, 2012, 09:31 AM
    Did the other outlets work properly before you replaced that first outlet? If so - are you sure that the metal "bridge" that connects the two screws on either side of the outlet are intact? Finally - if you have an outlet tester (the kind that has indicator lights to show the status of the wiring) - what does it show? You can get one for just a few bucks at your local hardware store.
    Luther42's Avatar
    Luther42 Posts: 5, Reputation: 1
    New Member
     
    #5

    Sep 13, 2012, 11:01 AM
    Yes. Everything worked before I replaced the outlet. The new outlet that I installed has power, but some of the other outlets in the same circuit do not. Also some do. So, I'm assuming the one I replaced is in the middle of the circuit and the ones that don't work are at the end. Correct?
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #6

    Sep 16, 2012, 08:47 AM
    Have you worked on any other outlets, switches, etc ? Also test hot to ground at the other receptacles and tell us what you find.
    Luther42's Avatar
    Luther42 Posts: 5, Reputation: 1
    New Member
     
    #7

    Sep 17, 2012, 08:22 AM
    Quote Originally Posted by shuntripper View Post
    have you worked on any other outlets, switches, etc ? also test hot to ground at the other receptacles and tell us what you find.
    No. Just this one. Tested all outlets and switches "down the line" and there is no power.
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #8

    Sep 17, 2012, 07:18 PM
    Humor me here. This is a new duplex receptacle like this?
    http://www.cesco.com/resources/07847...ctImageURL.jpg
    See the little piece of brass between the two screws on the side? Is it still there on yours? On both sides? This has already been asked, just differently.
    You need a voltage tester, sounds like you have one. Turn the circuit off and ease the receptacle out of the box and let the wire support it, then turn the circuit back on.
    Test between each hot screw and the ground to see if they are both hot when the wire is hooked up, if one is not hot, the brass is not connecting between the two screws
    IF you find voltage on BOTH of the hot screws, test for voltage between a hot screw and each white(neutral screw) that will tell you if the neutral is good where it leaves the box

    Please tell me what you find
    Luther42's Avatar
    Luther42 Posts: 5, Reputation: 1
    New Member
     
    #9

    Sep 18, 2012, 07:37 AM
    I've done all that and it's all correct. The outlet itself is fine. It's everything beyond the outlet on the same circuit that doesn't work (a switch that controls overhead light and two more outlets and a double switch which controls two separate outside lights). By the way, the two outlets that don't work are both "end of circut". That is: they both only have two wires going to them
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #10

    Sep 18, 2012, 06:36 PM
    Quote Originally Posted by Luther42 View Post
    I've done all that and it's all correct. The outlet itself is fine. It's everything beyond the outlet on the same circut that doesn't work (a switch that controls overhead light and two more outlets and a double switch which controls two separate outside lights). By the way, the two outlets that don't work are both "end of circut". That is: they both only have two wires going to them
    The fact that the replaced one is working and sending power out/downstream tells you that the problem is at another location,
    You now need to check power in the same manner that I just indicated at the nonfunctioning locations.First check all the connections, wirenuts included, with the circuit turned off, before applying power and checking it hot.
    If you find no power at all in the nonfunctioning devices' boxes, the next step is to troubleshoot the remaining boxes on the same circuit that ARE functioning,
    When checking wirenuts in junction boxes, (circuit off) test them by tugging on each wire or disassembling the junctions one at a time and carefully re-wirenutting them, sooner or later the problem will reveal itself.

    Before you start, The best way to make up receptacles in a professional manner is NOT to use the receptacle as a wire connector. Take the incoming hot and all outgoing wires that need to be energized as they go to the next device ( not switched wires going from a switch to a light fixture for example, that is a switch leg) and wire nut them together with one more short piece of wire that will go to the device. This is called "tailing out" the wire. Do the same with the neutrals (white) and usually the ground wires are already done this way or with a crimp sleeve. Tuck the wire nuts into the back of the box, now you have much less wire to force into the box with the outlet.
    Done this way, the entire load downstream is not carried by that little piece of brass between the screws, I never put more than one wire to either screw on receptacles.

    Avoid push in connections like the plague. Those devices are the absolute cheapest c##p sold.

    Doubling and tripling wires into the back of a receptacle is done a lot in residential jobs because the profit margin is so small anymore, every effort is made to reduce the time it takes to get a job done, and wirenuts aren't free either. This is mechanically better, I like Ideal 341 and 452 wirenuts for most makeup in junction boxes, you might want a couple of grey, or blue ones (bigger) occasionally.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Convert Electric Dryer outlet to regular outlet [ 8 Answers ]

I just bought a gas dryer, leaving a funky 3 pronged outlet unused. The outlet was connected to the fuse box as a single circuit and I would like to let the new gas outlet take advantage of this. Is there any problem replacing the 'funky' electric dryer outlet to a regular three pronged outlet,...

Plumbing directions for converting floor drain outlet toilet to back outlet [ 3 Answers ]

Former home remodeler, and fairly capable on general plumbing. How do I convert floor discharge outlet to back outlet for Briggs toilet?

Easier way to convert regular (assume 110v outlet) to 3 flat prong 125v/250v outlet? [ 3 Answers ]

I bought an electric clothes dryer thinking it would work with the regular outlets in apt. However, and no wonder the guy left in a hurry and got angry when I asked to return it, get money back, the end of the dryer plug is 3 flat prongs, with a sticker that says it is 125v/250v. Without rewiring...

Wall switch controlling a outlet,want to use outlet to control ceiling fan [ 3 Answers ]

I Have a wall swich that currently controls a baseboard outlet. The Wall switch has a white,black, ground coming in from the top of the box-- and a white,black,red,ground coming in from the bottom of the box. The two blacks are tied together/two whites tied together... the red goes to the switch...

Converting regular 3 prong electrical outlet to dryer outlet [ 3 Answers ]

We just bought a stacking washer and dryer and now the electrical cord on the dryer won't reach down to the existing dryer outlet. Is there any way to convert a regular 3 prong outlet that is close enough into a dryer outlet?


View more questions Search