    Sauna heater trips GFI intermittently
    I have tested the resistance between the neutral and ground terminal of my sauna heater, when disconnected from mains and get a reading of some 30 M ohms. The trip cuts out only occasionally . When I remove the earth wire from the sauna heater there is no more tripping but I am not happy to leave I like that. Nothing else on the circuit trips out.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Aug 27, 2012, 03:22 AM
    The resistance of neutral to ground should be almost "0"...
    And you are right, "NEVER" disconnect the equipment ground...
    If the GFCI breaker is tripping you may have a potential hazard that should
    Be fixed or you may need a new GFCI. Older model GFCI breakers from the 90's
    Did have some problems...
    Consider hiring a good electrician.
    MervynMerv's Avatar
    MervynMerv Posts: 4, Reputation: 1
    New Member
     
    #3

    Aug 27, 2012, 05:25 AM
    Thanks for the reply.I am fitting a new double pole GFCI tomorrow the original ones are all early ninetys. Surely earth neutral resistance of 30 meg ohms should be negligible . I think the trips are too sensitive for sauna heaters and water heaters etc. I am hoping that a new one with nothing else on the circuit will improve the situation .
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #4

    Aug 27, 2012, 05:50 AM
    Merv,
    At your main electrical service the neutral is bonded to the ground... therefore there should be very "low" resistance between them (theoretically zero)... if you really have 30M ohms you have a dangerous problem that "needs" to be corrected!
    MervynMerv's Avatar
    MervynMerv Posts: 4, Reputation: 1
    New Member
     
    #5

    Aug 28, 2012, 05:51 AM
    Quote Originally Posted by hfcarson View Post
    Merv,
    At your main electrical service the neutral is bonded to the ground...therefore there should be very "low" resistance between them (theoretically zero)....if you really have 30M ohms you have a dangerous problem that "needs" to be corrected!
    Thanks, the main electrical service neutral is bonded to ground as you say
    I meant the high resistance was present between neutral and ground on the sauna heater when completely disconnected from mains . This would be correct. I fitted a new double pole gfi today. Tested and working properly. Time will tell if there is a real problem with the sauna heater it's self. Interestingly .I could not see where the earth and neutral were connected behind the main electrical service board. Are they tied inside the electric meter? Which of course is tamper proof .
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #6

    Aug 28, 2012, 07:37 AM
    Typically yes... inside the meter, then at the "first" overcurrent device.
    If the neutral bar in the panel is not physically connected to ground, the ground wire, grounding electrode conductor and the panel enclosure, it should be.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

GFI trips [ 3 Answers ]

We just moved the old refrigerator to the garage to use for water and soda. The outlet is about six feet away from the refrigerator. I am using a light duty extension cord and after a few hours the gfi trips. If I us the same extension cord from a regular outlet in the house no problems. Is the...

GFI trips intermittently [ 14 Answers ]

My daughter has a gfi that controls two receptacles and a light switch in her bathroom. She has owned the house for about a year and had no problems with the GFI. However over the last two months, the GFI has started to trip intermittently. She told me it does not rip when being used - just some...

New Sauna Heater Trips GFI When Desired Temperature is reached [ 5 Answers ]

I have just installed a new outdoor sauna. The new sauna heater trips the GFI breaker when the thermostat shuts the heater off after reaching the specified temperature. I have a 50 amp GFI breaker in the house 200amp load box. From there I ran #6 wire for 120 feet to an external weather proof...