    Is rigid conduit okay for electric to swimming pool?
    Is it okay to use rigid conduit, buried 6 inches, to get power to swimming pool pump and filter? The soil between the pool and house is so full of large rock that I cannot dig an 18-inch deep trench for PVC conduit without using a track-hoe. The distance from pool to house is about 25 feet and the ground is level. There currently is no deck between the house and pool. Is there another option for running the electric without an 18-inch trench that I haven't considered?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 18, 2012, 03:23 AM
    Yes, you may use steel rigid conduit buried 6 inches deep. For additional protection, you may want to have some concrete poured over the conduit, but not necessary.

    Be sure to have the conduit 6 in deep to the top of the conduit.

    Other items to consider:

    Be sure the conduit connections are wrench tight.

    Do not use any pipe dope on the threads of any electrical conduit.

    Be sure to use an insulated green equipment grounding conductor.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electric Service to a Swimming Pool [ 0 Answers ]

I need to run a new line from my eletrical box to the swimming pool for a switchless pool pump. The motor voltage is 208-230/115 and amps 6.4-5.9/11.8. What type of wire do I need to use to for a direct wire or to wire a twist plug outlet? What type of breaker will I need for this same installation?

Rigid conduit above ground application [ 4 Answers ]

Does the NEC require the use of pipe dope or Teflon tape on the threads of rigid conduit?

What is the distance between supports for 88mm rigid conduit? [ 1 Answers ]

What is the distance between supports for 88mm rigid conduit?

Bending rigid 1-1/4" electrical conduit [ 1 Answers ]

Where in the greater San Jose, CA can I get an 1-1/4" electrical rigid conduit bent to specifications?

Minimum rigid conduit size [ 2 Answers ]

What is the minimum conduit size for 3 -#2 copper wires to a service panel?


View more questions Search