    4th_stooge's Avatar
    4th_stooge Posts: 8, Reputation: 1
    New Member
     
    #1

    Aug 4, 2012, 11:08 AM
    Reliance transfer switch alternative
    Purchased generator for mom’s house for outage use, electrical panel is encased on outer wall with stucco so don’t want to go reliance transfer system. Here is my alternative plan for this issue. There is a covered patio outside the kitchen and dining area, which would be her mainstay during power outage. Thinking of putting a L14-30 plug on the outside wall and two 5-15 receptacles on the inside which would feed off the L14-30 plug on the outside. I would use the 2 hot leads of the L14-30p to power each of the 5-15r’s (one leg of hot for each) and splice ground and neutral. This would be totally off the grid and no danger to any line workers. Also can leave a light on in living room area as indicator of main power being back on. Am I on the right track here? Is there something else I need to do? Any and all input is greatly appreciated.
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #2

    Aug 4, 2012, 06:31 PM
    NO, that sound well thought out, but it isn't right, probably not legal either. A company called Generator Interlock Technology, makes a real nice interlock kit for most panels out there. They cost about $150. Basically you put a 2 pole 30 amp breaker at the top of the panel. Wire that breaker to a 30 inlet box that has an L14-30 inlet in it. The interlock is UL listed, and allows the main OR the 2p 30 breaker, but never both. I highly recommend them.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Aug 4, 2012, 06:42 PM
    ..
    This would be totally off the grid and no danger to any line workers
    I don't see any difference, electrical, in this plan and running an extension cord through the window.

    Generator should be far enough away from the house to avoid any concerns about carbon monoxide.
    4th_stooge's Avatar
    4th_stooge Posts: 8, Reputation: 1
    New Member
     
    #4

    Aug 4, 2012, 09:01 PM
    Even though generator has 30amp breaker, would it be safer if I go width GFI plugs on the inside?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Aug 5, 2012, 02:28 AM
    You cannot use a 30 amp breaker to protect 15 amp receptacles. Using GFI devices does not eliminate the need for 15 amp protection for the 15 amp receptacles.


    The genset should have 5-15R devices with 15 amp breakers built in. If all it has is the L14-30 outlet, then the interlock and connect to panel is the best method for several reasons.
    4th_stooge's Avatar
    4th_stooge Posts: 8, Reputation: 1
    New Member
     
    #6

    Aug 5, 2012, 10:26 AM
    Quote Originally Posted by tkrussell View Post
    You cannot use a 30 amp breaker to protect 15 amp receptacles. Using GFI devices does not eliminate the need for 15 amp protection for the 15 amp receptacles.


    The genset should have 5-15R devices with 15 amp breakers built in. If all it has is the L14-30 outlet, then the interlock and connect to panel is the best method for several reasons.
    Thanks, that makes perfectly good sense. Genset does have 5-15R's so I would be better off using those to go through the wall. Patio wall has wood siding so that would eliminate having to bust up the stucco @ the elect. Panel. Anything else I should be aware of ?
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #7

    Aug 5, 2012, 10:37 AM
    Quote Originally Posted by 4th_stooge View Post
    Thanks, that makes perfectly good sense. Genset does have 5-15R's so I would be better off using those to go through the wall. Patio wall has wood siding so that would eliminate having to bust up the stucco @ the elect. panel. Anything else I should be aware of ?
    The 5-15R's are standard outletts. They are convience outlets, not inenteded to feed a disribution panel. The only way to wire the panel is using a L14-30 twist lock. If you don't want to ruin the exterior wall, mount the reliance panel inside. Why can't you do that? Then when attaching the cord run it under a garage door, or through a window.
    4th_stooge's Avatar
    4th_stooge Posts: 8, Reputation: 1
    New Member
     
    #8

    Aug 5, 2012, 11:42 AM
    I am trying to get away from wiring to the elect panel if possible. It is mounted outside, encased in stucco at an awkward part of the house, if no safe alternative way is available I will go with transfer switch to elect panel. Outside patio area would be the most easiest way to go being it is just outside kitchen (refrigerator) which her main concern. Don't really want to run extension cord through kitchen window but until I get issue resolved that is the way to go right now. I really do appreciate any and all suggestions, thanks...
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #9

    Aug 5, 2012, 12:45 PM
    There is no safe way to hook it up without wiring a transfer switch or panel interlock. Any other way creates the possibility of creating a backfeed on the line, posing a threat to anyone working to restore power. Even if YOU know what you're doing, and are certain you will shut of the main, ijt only takes forgetting 1 time to kill somebody. Please, for the sake of your lineworkers, wire the tansfer switch or interlock correctly. This isn't something that you can cut corners on.
    4th_stooge's Avatar
    4th_stooge Posts: 8, Reputation: 1
    New Member
     
    #10

    Aug 5, 2012, 02:09 PM
    Quote Originally Posted by mike 165278 View Post
    There is no safe way to hook it up without wiring a transfer switch or panel interlock. Any other way creates the possibility of creating a backfeed on the line, posing a threat to anyone working to restore power. Even if YOU know what you're doing, and are certain you will shut of the main, ijt only takes forgetting 1 time to kill somebody. Please, for the sake of your lineworkers, wire the tansfer switch or interlock correctly. This isn't something that you can cut corners on.
    Don't know if you read my original question or not but my initial plan was to put a plug on the outside wall and the immediate inside wall to get power inside the house. Like a mini transfer station totally off the grid. Everything would be encased in proper boxes and wires in proper conduit. I by all means will not use any existing plugs that is wired to the elect panel, that would be insane. Maybe I didn't explain my intentions in the beginning. I would use 5-15R's both inside and outside that would feed from the generator's 5-15R which is surge protected.
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #11

    Aug 5, 2012, 02:31 PM
    Quote Originally Posted by 4th_stooge View Post
    don't know if you read my original question or not but my initial plan was to put a plug on the outside wall and the immediate inside wall to get power inside the house. like a mini transfer station totally off the grid. everything would be encased in proper boxes and wires in proper conduit. I by all means will not use any existing plugs that is wired to the elect panel, that would be insane. maybe I didn't explain my intentions in the beginning. I would use 5-15R's both inside and outside that would feed from the generator's 5-15R which is surge protected.
    That would only give you 15 amps and only power 1 phase. Also how would you prevent the power from flowing back to the street, or stop you generator from cooking when you get street power back. To do it right, the only thing you need to put outside would be an inlet box, it's small roughly a 6" square, 4" deep. If that's too big, you can cut an old work deep box in, or a deep single gang Bell box. Just put a L14-30 male inlet and a outdoor cover and you're all set. If that doesn't solve it then the question isn't clear to me. I thought the issue was not wanting to ruin the stucco. You can put the correct 30A receptacle in the same box you are planning on putting a duplex outlet. Put everything else inside...
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #12

    Aug 5, 2012, 02:39 PM
    Oh, the panel is encased in stucco... Hmmm
    4th_stooge's Avatar
    4th_stooge Posts: 8, Reputation: 1
    New Member
     
    #13

    Aug 5, 2012, 03:57 PM
    Quote Originally Posted by mike 165278 View Post
    Oh, the panel is encased in stucco.... Hmmm
    There would be no possible way to get power out into the street or power back to the generator when main power is back on. It would be like running 4 extension cords from the generator's two 5-15r's through a hole in the wall and to the refrig, fan, TV,radio,etc. The only thing is I am replacing the hole in the wall with two 5-15r's on outside wall that will be directly connected to the two 5-15r's on the inside of the wall. All will be encased in proper outlet boxes and wires in proper conduit from outlet box to outlet box. I greatly appreciate and totally understand your safety concerns. So is this something that could possibly work? Keep in mind that there is wood siding in patio area and not stucco, that is why it would be easier for me to go that route.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I use 8-3 wires for a transfer switch? [ 1 Answers ]

I've thye Gen/Trac 30 amps TRANSFER SWITCH. It will be installed in the basement with the main power breaker. The outside inlet will be at the out side wall, about 40 feet to the transfer switch. I will then use the 25 feet extension cord to run from the generator to the inlet box. Can I use...

Reliance 30216A transfer switch vs a GenTran 30216V [ 1 Answers ]

What is the difference between these two generator transfer switches other than cost ($240 vs $200)?

Transfer Switch [ 2 Answers ]

How do I wire a tranfur switch for a portable 6300 watt generator coming from the Main panal to the tran tranfur switch do I need a subpanal to also can you give me A diagram also For this I would bring power from a 60 amp breaker in main panal I only want to run afew things...

Transfer Switch [ 3 Answers ]

Ok I am looking to add a transfer switch so I can run my generator when the power is out. I have always been told that my transfer switch needs to be rated higher then my generator's output. The problem is my generator has two output rating stated. In other words, a constance rating of 5,550 kw...

Transfer switch [ 6 Answers ]

I’ve recently purchased a Guardian 13kw standby generator with a transfer switch and load center panel. I have a couple of questions 1. The transfer panel had a total of 205 amps through 12 various breakers in it, can I replace some of them as long as I don’t go over the original 205 amps and use...


View more questions Search