    Grounding system connections
    I am putting in a generator with an automatic transfer switch (ATS). The ATS will go between the meter and what is currently the main panel. The ATS has a service disconnect breaker and will become the "main" panel, and what is currently the main will become a "sub" or distribution center. I will pose my question referring to the two boxes as the ATS and the "sub," respectively. Currently there is a grounding cable from the "sub" running outside to a pair of grounding rods in the earth, and a grounding cable completely inside that runs to the copper cold water pipe where it comes into the house. Currently the neutral bus and the ground bus in the sub are bonded, but I will be removing that connection when the ATS gets installed; the neutral will be grounded in the ATS.

    Now, the question I have is, will I have to remove the grounds in the sub that go to the water pipe and the ground rods and place them into the ATS (which will be problematic, since they will not reach as is) or will it be sufficient to just run a ground wire from the ATS to the ground bus in the sub?

    Follow-up question, if I need to move the ground wires out of the sub and into the ATS, can I splice the ground wires? They are both what looks to me like bare, stranded #6 copper, but I am not totally sure about the size.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 4, 2012, 03:00 AM
    The neutral and grounding can only be electrically connected, "bonded", at the enclosure that contains the Main Breaker, or before the main. After the Main, the neutral must be insulated and isolated from equipment grounding.

    Grounding electrode conductors must be continuous, or if spliced , must be irreversible connection, such as a compression crimp connector.

    You can buy compression connectors at electrical distributors, and some loan or rent out the crimp tool.

    Therefore, you cannot use the screws in the ground bar in the "sub" to splice the grounding electrode conductor.

    The grounding electrode conductor is probably #6 copper,but you need to be sure. Cut off a sample and bring it with you when you buy more wire and the crimp connectors.

    Good time to check the connections to ground rods and water pipe.
    User113's Avatar
    User113 Posts: 6, Reputation: 1
    New Member
     
    #3

    Aug 4, 2012, 05:43 AM
    Thanks. That was what I thought, but I was hoping a ground jumper would work. I appreciate the info about the compression connectors. That will be much easier (and cheaper) than re-threading 50 feet of #6 copper just to go another 4 feet.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Verifying Grounding Connections [ 6 Answers ]

I recently rewired my basement workshop. I put in a short section of EMT to carry wires from the overhead joist down to a two-gang receptacle box and then out again to second two gang receptacle box. I ran two circuits so I could control which tools were on which circuits more easily. I...

Grounding Electrode system [ 9 Answers ]

What's makes up a grounding electrode system? Then is an EGC apart of this system? If not, explain how it isn't? :cool:

Grounding System [ 1 Answers ]

How was the grounding system working when a ground fault appear, and where the fault current flow?:)

Grounding system [ 1 Answers ]

What is more effective in industrial application.. the HRG (high resistant grounding) system or the low resistant grounding system?

Grounding of an electrical system [ 1 Answers ]

I read the info about ground & believe I understand why it needs to be done & how to do it. My question is this. In the current set up for my house my panel is grounded to the gas system not the water system. The water for the house is nowhere near the electric service closet so grounding to it...


View more questions Search