    AAV or full vent riser?
    I just had major construction done on my house and all the walls around the kitchen were open (including the ceiling). The counters and sink were finally installed and I tested the sink. I noticed it drained very slowly like a clogged sink. I looked under the sink in the cabinet and noticed that there was a short vent with a vent cap. I was surprised to see this since all the walls were open why not run a proper vent stack. Well I pulled the cap off the vent and the sink drained immediately. I put it back on and it made some funny clicking noises.

    Still wondering why the plumber (sub contractor) didn't run a full stack. Was he being lazy or cheap? Is there a preference between full stack or AAV if you have the ability to run a full stack to the roof?

    I just want to get my facts straight before I make an issue of this with the contractor.

    Thanks
    Marc
    Long Island, NY
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Jul 30, 2012, 11:03 AM
    Hi Marc

    I don't think they allow AAVS in New York... hmmm.

    Was a plumbing permit pulled on the job? If a plumbing permit was pulled then AAVs must be approved in your area and you are stuck with what you have there. In this case, it sounds like you need to replace the defective AAV and/or snake the drain line.

    If there was no permit pulled then you are also in a tough situation, but the first thing to do would be to call a local plumbing inspector and just ask him if you can use an AAV in your state (don't think so, as stated). If no AAVs allowed then you talk to the contractor and tell him that you may not have pulled permits on the job but you still expected all codes to be adhered, too.

    Finally, it is always a preference to run a non-mechanical vent (vent stack) vs a mechanical vent that can fail... always!

    Get back to us with more details...

    Mark
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #3

    Jul 30, 2012, 11:20 AM
    Is there a preference between full stack or AAV if you have the ability to run a full stack to the roof?
    Marks answer was bang on.
    Finally, it is always a preference to run a non-mechanical vent (vent stack) vs a meachanical vent that can fail.
    And that's exactly what I think you have. A failed AAV.
    You told me yourself when you said,
    I pulled the cap off the vent and the sink drained immediately.
    There's no doubt in my mind that if you'd replace the AAV your sink would drain. Whether it's legal or not is up to your inspector. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Do I need a vent or AAV valve for a washer drain? [ 13 Answers ]

I've read a bunch of threads on problems people have with washing machine water backing up around the drain stack. In particular the posts by hkstroud and speedball1 have been very informative. I have a 1 1/2" pvc drain stack that is above the height of the washer. It also has a trap before...

AAV needed for basement full bath? [ 9 Answers ]

I had a full basement roughed in, they added a AAV (Oatey) to the vent stack. If I am adding a toilet, sink and shower can I use the AAV only? The actual vent is about 50' away on the other side of the house. Please take a look at the picture.

Installing an aav (pro vent) in a mobile home [ 4 Answers ]

My kitchen sink was draining slowly and by process of elimination I concluded it must be the aav.as I removed the old one the drain started working properly.I replaced it with a new one and it worked normal for a day and then the sink started backing up again and draining really slow.it looks as if...

How to use a AAV vent [ 2 Answers ]

In the attachement, which is the correct connection for an AAV vent. The standpipe is for a washing machine discharge. Assume the pipe is 2 inches. I assume (from prior answer) there is a desire to place vent vertically close to the p-trap (2 to 5 feet). What's the best vertical distance to...

Difference between AAV and cheap vent valve? [ 10 Answers ]

What's the difference between an AAV and a cheap vent valve? I'm referring to the $3.00 1 1/2 inch vents with a one way rubber check valve that I believe are sold to vent kitchen sinks, and the more expensive $20.00 AAV Air Admittance Valves like a Studor. They appear to do the same function. I...


View more questions Search