    haroldw's Avatar
    haroldw Posts: 1, Reputation: 1
    New Member
     
    #1

    Jul 24, 2012, 08:10 AM
    Plumbing questions answered free
    I have a lawn sprinkler system 3 zones that in summer run in total approximately 1 hour. The system is scheduled to run at 5:00 a.m. When I go to shower after the system has water or use any hot water supply the water runs slowly for a few seconds then I hear a pop sound and then it runs normal. It’s as if there’s an air bubble in the line. This only happens after using the lawn sprinklers no other water source. I’ve already installed a an anti-pipe knock devise in the sprinkler line and a pressure regulator in the water main line set at 60-65 lbs. Anyone know what’s causing the problem with the hot water line?

    Thanks,
    Harold
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Jul 24, 2012, 08:38 AM
    Hi Harold

    With what you have presented I am thinking you could have an issue with the HEAT TRAP NIPPLE installed at most water heaters nowadays.

    Check your heater nipples and see if they look anything like in my pictures below (look for the indented line around the nipple).

    If you have these nipples it is possible that the heat trap ball is getting hung up in the nipple. If this is the case you just need to remove the heat trap nipple(s) and install regular dielectric nipples at the heater.

    You or a plumber can install a heat trap by installing a simple UTURN in the hot water pipe... can discuss more if you want, OK?

    Mark
    Attached Images
      
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #3

    Jul 24, 2012, 08:48 AM
    I think Mark nailed it! Check the nipples, (see image) and either replace with a 3/4 X 3" brass nipple or build your own heat trap.(see image) Good luck, Tom
    Attached Images
      

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Plumbing questions answered free? [ 12 Answers ]

I have a Kohler kitche faucet that is 12 years old. The issue is the hand hels sprayer nozzle you you pull out from the counter top. When we go to use it it just piddles out a little bit of water. I have taken the hand held part of and cleaned it with CLR. That didn't help. Will I need to replace...

Plumbing questions answered free [ 8 Answers ]

Water pressure was fine until we replace our hot water heater.Now our water pressure is a trickle and is getting worse.

Plumbing questions answered free [ 1 Answers ]

Kitchen sink is draining very slow on both sides. When water is draining it will go to the other side and drain very slowly. It happens to both sides. We have used professional gel and have replaced several sections of PVC pipe under the sink and in the basement. The problem still persists. ...

Plumbing questions answered free [ 2 Answers ]

I have to replace my dishwasher. I have a valve assembly as shown in : http://tinypic.com/view.php?pic=4htu9&s=5 It has lines and tow valves one to the faucet and one to the dishwasher. Neither shuts off anything. What is this??

Free plumbing questions answered? [ 0 Answers ]

I am replacing an existing gas logs with a new set. The existing had a copper pipe from the wall of the ceramic box And a shutoff valve it ran under the existing logs about 1 foot To the other side of box to the controls. The new logs I bought a flexible stainless steel pipe that says It OK...


View more questions Search