    Vanity Light -- unexpected results!
    Greetings!

    Thank You (in advance). I appreciate the help! A lot! Thank you very much!

    I just installed a new 4-light vanity fixture (or tried to anyway). An "out with the old and in with the new" job. Old vanity had black/white/ground. New vanity has black/white/ground. It seemed so easy.

    • (vanity) black wire to (house) tan wire
    • (vanity) white wire to 2nd (house) tan wire
    • ground wire to ground wire
    • existing (house) wire to (house) wire connected with a wire nut----untouched


    When I turn on the switch the vanity lights (four) are very dim... like night light and/or lamp kind of dim. I tried the 75W Frosted bulbs that came with the new vanity light. Plus, I tried 100W regular plain ole bulbs. Oddly, a nearby overhead light (on the same switch) comes on as normal.

    If I remove 3 of the 4 bulbs the remaining light brightens and the overhead light dims to nearly nothing. If I remove all 4 bulbs the overhead light goes out, too.

    I don't understand...
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jul 11, 2012, 11:00 PM
    existing (house) wire to (house) wire connected with a wire nut----untouched
    What color are those wires?
    suzier's Avatar
    suzier Posts: 6, Reputation: 1
    New Member
     
    #3

    Jul 11, 2012, 11:22 PM
    Quote Originally Posted by hkstroud View Post
    What color are those wires?
    Unfortunately they are both tan. :(
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Jul 11, 2012, 11:55 PM
    Colors not logical.

    Connect black of vaninty to the two untouched wires. Connect the two wires you say are tan but I suspect are really discolored white, together with the white of the vanity.

    Symptoms you describe indicate the two tans are really the neutral. Power is going through each light bulb in a series, that is to say that power is going through one bulb to get to the next.

    Appearently you did not note the connections when you remove the old fixture. Black wire to fixture came loose from the two house wires (with the wire nut) and you did not notice. These wires should be black.

    To restate the above.

    The two house wires presently connect together with a wire nut are the hots and should be black. The two tan (discolored whites) are the neutrals.

    Connect all blacks together. Connect all whites together.
    suzier's Avatar
    suzier Posts: 6, Reputation: 1
    New Member
     
    #5

    Jul 12, 2012, 06:49 PM
    Quote Originally Posted by hkstroud View Post
    Colors not logical.

    Connect black of vaninty to the two untouched wires. Connect the two wires you say are tan but I suspect are really discolored white, together with the white of the vanity.
    You were correct on every single point!

    The colors were not logical at all! In reality they were almost brown. ALL OF THEM. They now have been marked correctly.

    When I removed the old fixture, two of the three existing wire nuts came apart coming out of the fixture box. I assumed the one in-tact had indeed stayed in-tact. WRONG! As you suspected connecting the black was the ticket!

    Now I'm off to buy some dimmer bulbs... not sure I wanted to see THAT much!

    Thank you very much for you help!!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom Vanity Light [ 12 Answers ]

I am trying to install a vanity light. There are 4 green wires tied in a bundle, 4 black wires tied in a bundle, one loose green wire and one loose bare wire. The new light has one white wire, one black wire and one bare wire. I connected the wires and all I get is direct current to the fixture....

Replace Vanity Light with Convenience Outlet with Light Only [ 2 Answers ]

I am replacing an older style vanity light in a guest bathroom. The old light has a convenience outlet built into the light fixture base. The new light has only a black, white and ground wire. The painters removed the old light so I do not know how it was connected. The wires coming from the...

Excel 2003 - using Enter key has unexpected results [ 3 Answers ]

When I press the Enter key in Excel 2003 the entire page moves instead of moving the cell location. The Tab key also moves the page instead of moving the cell location. Any help with this would be appreciated. Thanks

Vanity Light [ 1 Answers ]

Recently I changed the vanity light in the bathroom. When I turned on the light I realized the breaker had tripped. I reset the breaker and all was fine for a couple days... the breaker tripped again. So I reset it and the same thing... 2 days later it tripped. I removed the light and can find...

Vanity Light Troubleshooting [ 3 Answers ]

I have a six-bulb vanity light bar in my bathroom. One of the lights will not work even with a new bulb installed. How do I disassemble the light fixture to determine if there is a loose wire? I do not see any screws that hold the decorative piece in place, so any information on how these...


View more questions Search