Originally Posted by
mikect05
can I put a put a double 90 upside down in a vent installation.
In other words have the the vent coming down and sweeping 90 degrees in two different directions.
Thanks
If you are asking if you can vent downwards, absolutely not! You cannot even vent laterally with an even grade! It must be on a grade .slope upwards from the heating appliance to the chimney connection at no less than 1/4" per foot of horizontal run
Flue vent connectors for "B" or "L" Vents: A vent connector connects gas equipment to a flue or chimney. Appliances having draft hoods and installed in an attic or concealed space must use Type B or L connectors. Appliances installed in basements can use Type B or Type L or metal pipe (.0304" thick) or aluminum pipe (.012" thick). Gas fired equipment should not be connected to any flue serving solid fuel appliances.
Multiple gas vents into a single flue: Where two or more vent connectors enter a common gas vent, chimney flue or single wall metal pipe, the smaller connector shall enter at the highest level consistent with available headroom and clearance to combustibles. Avoid unnecessary bends and secure all joints with sheet metal screws or other approved means.
Metal flue vent connectors should also be joined with the female (wider) ends facing "up" so that condensate and creosote that may form inside of the flue connector remain inside of the flue pipe. Our photo (above right) shows that foil tape was used to join two flue vent connector pipes of different diameters from a gas fired heating appliance . Foil tape is not a suitable substitute for the necessary adapter to join the two different diameter flue vent connectors.
Horizontal vent length limits: The horizontal length of a vent connector to a natural draft chimney or vent serving a single draft hood appliance shall not be more that 75% of the height of the vertical portion of the chimney above the connector. [NFPA 1992 (7.10.10)].
The maximum horizontal length of vent connectors per the GAMA tables is limited to 1.5 feet per inch of diameter with a provision of a 10% reduction in capacity for each multiple of the length permitted. The venting tables must be consulted to size an adequate venting system.
Watch out: allowable flue vent connector length calculation can be a bit more complex than that rule of thumb,
Slope upwards from the heating appliance to the chimney connection at no less than 1/4" per foot of horizontal run
Be kept as short as possible - long runs get cool, produce condensate, soot and debris and rust and clogging
Have flue pipe sections joined by three screws (two screw joints easily separate to vent dangerous flue gases into the building.