    Lennox 10ACC-048-230-02 - Condenser fan not working - intermittently
    When the unit is turned on, everything functions perfectly. After running the unit approximately 30 minutes, the condenser fan stops working. If the air conditioner system is turned off for awhile (a reset), then the system works well for 30 minutes, then the condenser stops running. I replaced the capacitor. What could be causing the condenser fan to be in the state of intermittently that I described above?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jun 28, 2012, 09:00 AM
    Quote Originally Posted by wanaknow101 View Post
    When the unit is turned on, everything functions perfectly. After running the unit approximately 30 minutes, the condenser fan stops working. If the air conditioner system is turned off for awhile (a reset), then the system works well for 30 minutes, then the condenser stops running. I replaced the capacitor. What could be causing the condenser fan to be in the state of intermittently that I described above?
    The condenser fan motor contains a internal overload. After it trips it takes awhile for it to automatically reset and start to run. If the coil is not clean in the outside unit it can cause the motor to overheat and trip the overload. If the overload has tripped a lot it could be weak and then the motor will have to be replaced. If the motor is running backwards it will also cause it to overheat. You need to check all the above items and make a decision as to what is the cause of the problem then fix it.
    wanaknow101's Avatar
    wanaknow101 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 28, 2012, 09:27 AM
    Thanks for your response. The coil is clean (I made sure of that issue). Whenever the motor stops running, I can feel a lot of heat in the unit. How do I determine if the motor is rotating backward? Can a low freeon cause this issue? Is there a way to check if the motor is bad?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC condenser fan turning on and off intermittently [ 12 Answers ]

I just turned on the AC for the first time this season and I noticed that the condenser fan outdoors is continuously turning on and off intermittently, i.e.. on for three seconds, off for three seconds; on for three seconds, off for three seconds, etc. This is a Carrier unit. Any idea on how I...

1/6 HP 2-speed 1075 rpm 208/230 volt condenser fan motor wiring diagram [ 2 Answers ]

I am having trouble wiring the condenser fan motor in with capacitor and new contactor on a single phase 240V system. I have no wiring diagrams to go by as this condenser is 20 plus years old. The compressor will fire but I cannot get the fan motor to run even though it's wired off both sides of...

Condenser fan fails to start intermittently [ 1 Answers ]

Condenser fan sometimes fails to start (notably after its been running for some time). After I de-energize the unit for ~ 1/2 hr, it it then starts up. 1. Do I need to replace fan and capacitor? 2. The installed capacitor has 3 leads with a resistor across 2 terminals. Do I find a like...


View more questions Search