    GFCI Help
    I had a GFCI outlet in my basement that shorted out. I replaced it with a new GFCI outlet but now the outlet that supplies it (also a GFCI) from the upstairs bathroom does not work nor do the lights in the bathroom. However the two downstream outlets from the basement GFCI do work. What did I do wrong?
    smearcase's Avatar
    smearcase Posts: 2,392, Reputation: 316
    Ultra Member
     
    #2

    Jun 22, 2012, 05:01 PM
    It sounds like the outlets that you are calling downstream are actually the original source of power to the outlet you replaced.
    You may have attached the wrong conductors to the line side of the gfi. Remove the gfi that you replaced, test (if you have the proper testers and can do so safely)the wires and attach the wires that have voltage to the line side of the gfi and ensure that the wires that do not have voltage (with the outlet removed enitirely) should be placed on the load side of the gfi.
    There is also a possibility that some other part of the circuit was damaged when the gfi "shorted out. What caused that?
    Also, gfi's come with instructions. Are you certain that you have read and followed the instructions and checked the troubleshooting suggestions in those instructions?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Jun 23, 2012, 07:53 AM
    Are the 2 GFCI's connected line -line- or line-load? If line -load, you don't need a GFCI in the basement, it is protected from the first one.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gfci wiring and bathroom switch controlling the power on and off to gfci plug. [ 3 Answers ]

I got a concern caused by my brother in law, I have had to perform a bathroom reno and needed to upgrade the wall switches and install a gfci plug, well all wiring was OK till after the drywall went up and now, no power to vanity light(power is on wire as it goes through attic, nothing comes up at...

Can I put outside gfci, and laundry gfci outlets together on ciruit? [ 5 Answers ]

Hi, I am in the process of redoing my basement, adding a bathroom and laundry room. I would like to have one gfci protected outlet in the bathroom, one in the laundry room, and also add one outside (through the bathroom wall), I also would like a light in the shower stall which will need to be...

Changing 15 amp non-GFCI split to 20 Amp GFCI single (kitchen counters) [ 11 Answers ]

I have an older home and I am redoing the kitchen. The kitchen outlets are currently split ones as per the code of the day. They are presumably using 14 gauge wire. (or maybe it may be 12 since it is the 3 wire loomex) It is not practical to re-run the wire. One of them is quite close to a kitchen...

30amp GFCI to 50amp GFCI [ 1 Answers ]

I have a square D panel box with 200 amp service coming into the house. I have a square D 30 amp double pole gfci breaker that was put in last year for a hot tub. I am now getting a new hot tub, and it requires a 50amp gfci breaker. The 30amp currently in place says type/tipo HOM. It is...

When adding a GFCI disconnect for hottub, should I replace GFCI in service panel? [ 4 Answers ]

I have a hottub now but without a disconnect. Its simply a 6/3-50 amp wire that runs from the hottub to a 50amp GFCI inside the house main service panel. I want to install a disconnect 5-10 feet from the hottub. I bought a disconnect box that already has a GFCI inside of it. Should I have bought...


View more questions Search