    Neutral. Wire
    We have a duplex receptacle in a gem box recessed in a wall ( . 120v. 20 amp ). In a 6' greenfield whip dropped down
    The wall coming. From box in ceiling to gem box in the wall
    We have a black #12 for the hot. A. Black #12 with white tape on it to identify it to be the neutral and a green for the
    Ground. Will the black with white tape on it for identification
    To be neutral pass the electrical inspection? National code.
    Thanks!!
    Berry1201's Avatar
    Berry1201 Posts: 2, Reputation: 1
    New Member
     
    #2

    Jun 15, 2012, 10:10 AM
    120v 20amp duplex
    We have a 120v duplex receptacle in a drop ceiling (acoustical) . This is used for a 120v to 24 v transformer
    This intern feeds a time clock on the wall 6' a.f.f the 24v runs down wall to the clock. Does this meet national code if receptacle is above the ceiling??
    Thanks!!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jun 15, 2012, 10:36 AM
    The actual Code text for when a white wire is used as a hot reads:

    ...shall be permanently reidentified to indicate its use by painting or other effective means at its terminations and at each location where the conductor is visible and accessible.

    Black tape is not considered permanent, but the ruling will be up to the inspector.

    Cords of appliances, and I believe a clock with a 24 volt power pack that serves the clock applies here, are not to pass through structure, such as a suspended ceiling.

    Again, up to the final decision of the inspector.

    I say no to both.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jun 15, 2012, 07:30 PM
    With respect to the Black conductor with the white tape on it to identify it as a Neutral conductor.

    This is a flat out code violation. Neutral conductors smaller than 6 AWG must be either white, gray or any color other than green with three vertical white stripes to be considered as Neutral.

    Please reference NEC, Chapter 2, Article 200.6(A)
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Jun 16, 2012, 01:30 AM
    Good catch Don I read it completely backwards.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Misuse of ground wire as neutral return wire in old house [ 5 Answers ]

Here a problem where the "obvious" solution scares me, need some advice on how to best proceed. My home (built 1920 with knob and tube type wiring) has been upgraded over the years by prior owners, but in many place still has active current in the old wires, in other places it is spliced into a...

Is hot wire is not a neutral wire or vice versa in single phase two wire AC source? [ 1 Answers ]

I am a little bit confused why in AC single phase 2 wire source is merely classified the 1 wire as hot and other wire as neutral. The hot wire travels the current from the source to the load and going back the current to the source through the neutral wire. I know that in AC circuit, the signal or...

Connecting neutral wire to ground wire in breaker panel [ 3 Answers ]

Can the neutral wire be connected to the ground wire at the neutral bar in the breaker panel?

Neutral wire is hot(has voltage potential like the black wire) [ 5 Answers ]

Hi, The problem started at midnight last week. One of my line in the basement is starting to have issue whenever I connect a water pump or appliances to the outlets. Before I plug the appliance in, the neutral is neutral(zero voltage), but when I plug the appliance in, the neutral is now...


View more questions Search