    Hot / Ground Reversal
    We have several outlets on a circuit that test "hot/ground reversed" with a plug in receptacle tester - with the breaker turned off. With the breaker still turned off, we tested the one of the outlets with a multimeter, and read no voltage white to black, no voltage black to ground, and 120 volts white to ground.

    With the breaker turned on, all three LEDs on the tester light up, including the red one indicating a reversal. With a multimeter, we read 120 volts black to white, 120 volts white to ground, and 240 volts black to ground.

    The home is about 55 years old. The wiring in the subpanel is old 12-2 Romex with no ground. Some, but not all, of the wiring in the walls is newer, yellow 12-2 Romex with a ground that somebody (probably the homeowner) added recently. The wiring in this place really is quite a mess.

    Our job is to install a bathroom fan on the circuit described above - not to correct all the obvious electrical deficiencies. Does anyone have any ideas what might be causing the condition described above? The 240 volts from hot to ground has us especially puzzled (and concerned).

    - Mike M.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 5, 2012, 04:23 AM
    You should be concerned about the 240 volts to "ground".

    Along with a neutral and hot reversed, there is a serious miswire, or a broken shared neutral to cause the 240 volts.

    I have to assume if you know how to trace this condition you would not need to ask questions here.

    I need to strongly recommend that you hire an electrician to trace and repair these conditions you have.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    May 5, 2012, 07:15 AM
    Tk's nailed it, you can't get 240 volts to true ground, you can get 240 volts between both hot legs,
    That's where he mentions "a hot neutral reversed".
    Go to electrical panel and verify both hots are hot and 240 volts between them, and 120 volts between each hot to neutral and ground.
    It seems like maybe someone may have changed recepticles and didn't keep white wires on white screws, plus the open neutral as in a multicircuit.
    Has this problem been like this, or just started.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #4

    May 5, 2012, 12:45 PM
    I'm onboard with the OP hiring an electrician :D

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I use a ground wire for a ground and live black or hot wire at the same time? [ 8 Answers ]

I only have 3 wires from my ceiling to connect to my fan/light, the black, white and bare ground. No problems setting up in this room to only one switch but I would like to have the duel fan/light switch in like in my other rooms without having to pull a wire from the ceiling down to the switch,...

Receptacles hot to neutral show no volts, hot to ground show 120v [ 1 Answers ]

Replaced four receptacles in parallel, checked for loose wires. Checked the gfi breaker and 120v leaving the breaker. Tested all receptacles with voltmeter showing 120v between hot and ground, shows no voltage between hot and neutral. None of the receptacles work. Got any ideas?

Hot White and Hot Ground [ 3 Answers ]

House wiring power is Black(hot) and White(Neutral-Common Ground). House does not have separate ground wire. Installing vanity Light with GFIC Outlet between Light and toggle Switch. Using Type NM-B 14/2 w/ground Romex 600V manufactured by Southwire. At Switch using black and white(white is tagged...

Ground/Hot Wire Reversal [ 5 Answers ]

Ground/Hot Wire Reversal I have an electrical problem that has me completely stumped. There is a section of my house that has a series of 6 receptacles on it – 3 in the family room, 2 in the garage, and one outside. The outside receptacle is a GFCI (the only GFCI receptacle in the series). ...

Ground hot reversal [ 5 Answers ]

All outlets on one circuit read ground hot reversal when tested. Problem started with fan/light going out. I disconnected wires to fan/light; no voltage between black and white. I checked wall switch and ground wire is hot. Is this due to a hot to ground short in one of the outlets or something...


View more questions Search