    Air conditioning condensing unit problem
    I have a trane condensing unit.. It runs but there is no cold air into house
    Anyone know what might be wrong?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Apr 24, 2012, 09:54 AM
    Is the inside blower working?
    Is the outside Fan Running?
    Is the outside unit blowing up warm or cool air?
    jomas19's Avatar
    jomas19 Posts: 3, Reputation: 1
    New Member
     
    #3

    Apr 24, 2012, 10:01 AM
    The outside units huge fan is working, there is air coming through the vents but it isn't cold its more like the outside temperature
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Apr 24, 2012, 10:07 AM
    The compressor may not be kicking in?
    When the inside unit is cooling, the outside unit will blow out warm air.
    The compressor is under the fan in the outside unit, may just be the capacitor.
    jomas19's Avatar
    jomas19 Posts: 3, Reputation: 1
    New Member
     
    #5

    Apr 24, 2012, 10:12 AM
    Where is the capacitor? Can I change it? Thanks so much
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Apr 25, 2012, 07:00 AM
    It should be in the compartment where the wiring goes into. Their will also be a contactor(relay) in there.
    Identify connections and turn off power to the unit before working on it.
    You may see it bulging, burnt, or corroded, check connections.
    I have a tester for capacitors.
    Capacitors are cheap, not tough to install, may fix it. I am not a parts changer, but would try this if you have no way to test.
    Also capacitors can hold a charge, when you remove the wires with insulated needle nose pliers, touch all connections on capacitor with insulated screwdriver or something.
    The charge in a capacitor won't hurt you, but it may make your hand jerk across something sharp.
    Be Careful, Good Luck.
    thermalmedics's Avatar
    thermalmedics Posts: 153, Reputation: 13
    Junior Member
     
    #7

    Apr 25, 2012, 09:38 AM
    Truthfully, last year we had a tech in PHX killed in an attic when he brushed against a 7.5 MFD run capacitor with a sweaty ear.

    The charge these things pack can be deadly. Follow Stratmando's advice about discharging the run cap before touching the leads.

    Here are some video advice on how to swap them out and there is more on you tube.

    run capacitor problems - thermal-medics FREE online air conditioning repair and info site from Phoenix AZ

    https://www.youtube.com/watch?v=YVcWasNjsbY

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant air conditioning unit 310AAV/JAV blowing warm air? [ 1 Answers ]

The unit is 2yrs old. Also it has been turned off for two weeks. Checked the filter, very dirty, but a new one in. Still warm air only.

Air conditioning unit-heat pump-air smells moist [ 3 Answers ]

The air coming from my vents smell as if something may be wet. I know that sounds crazy, but could the air be passing through some moisture source? We have the heat on at the current time. Last week we had the air on, I smelled this same smell. The air filter had this particular smell on it, like...

Home air conditioning unit is running no air blowing from vents [ 5 Answers ]

My a/c unit runs but, no air coming through vents the temp in house stays the same. I looked at it on the roof and water is heavily dripping from it. The unit is off now

Air conditioning condensing unit won't come on. [ 1 Answers ]

Air conditioning condensing unit won't come on.. . there is a humming nosie so I know it's got power.

New condensing unit problem [ 1 Answers ]

I installed a new condensing unit and put freon in the unit, I am getting the same pressure on the high and low sides of the gauges. This leads me to believe that there is a compressor problem or that I put too much gas in it. I am reading 150 psi on the high side and the gauge is pinned on the low...


View more questions Search