    Can I Update My 100amp Panel To A 150 Amp Panel Using The Same Awg2 Al-Triple Wire
    Can I Update My 100amp Panel To A 150 Amp Panel Using The Same Awg2 Al-Triple Wire That's Coming Into My House From Meter? Or Will I Need To Update That Wire To A Larger Wire?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 3, 2012, 06:46 AM
    No, the feeder from the meter, and possibly the meter, plus the feeder conductors feeding the meter, all need to be changed to 150 amp rated.

    Look into changing to 200 amp service, 150 amp is an odd size.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I install a 150 amp sub panel to a 200 amp panel with the sub running (3) 50 amp [ 13 Answers ]

I have square D QO panel. I am adding a Stiebel 29 on demand water heater and it calls for (3) 50 amp 240V breakers. Can I add a subpanel that has (3) 50 amp breakers to tie into my existing 200 amp service? If so what gauge copper wire would connect the two and does Square D QO make a 150 amp...

Adding a second panel to my house 100amp what size wire do I need? [ 1 Answers ]

I am adding a second 100amp circuit panel box for an in-law apartment is 2-2-2 wire the right size since I have a ranch house and the wire will be around 100 feet long and running in the attic which is hot.

Can I put a 150 amp breaker in a 200 amp panel to feed a 150 amp sub panel? [ 8 Answers ]

Can I put a 150 amp breaker in a 200 amp panel to feed a 150 amp sub panel with a 200 amp service?


View more questions Search