    Goodman Heat Pump(New) showing very high pressures and blowing warm air in cool mode
    Heat pump is new install. When flipped to cool it is blowing warm air. I followed the wiring schematic again, and everything seems to be fine. The only major thing I am unsure of is the thermostat (Honeywell FocusPro TH6000). It says it is for either Conventional or Heat Pump, but I am used to there being a switch or program button to choose which one. This one just has one wiring bar with the color code for conventional on top and heat pump on bottom. I feel it has something to do with the reversing valve but I just can't trace it out. Can anyone give advice?
    thermalmedics's Avatar
    thermalmedics Posts: 153, Reputation: 13
    Junior Member
     
    #2

    Apr 2, 2012, 07:23 PM
    Usually an orange wire for the reversing valve (outdoor unit to the t-stat). You can trace that out in the outdoor unit.

    Sometimes programming the thermostat is the key. There is an option I thought on those Honeywells to energize reversing valve in heating or cooling

    If I'm not mistaken goodman reversing valves energize in cooling
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #3

    Apr 3, 2012, 04:54 PM
    I would start with the stat. You will need to get hold of the install instructions for the stat. The honeywell pro 6000 is compatible with many different systems and needs to be programmed specifically for your type of system, and of course wired correctly. I do know that the pro 6000 comes factory set for convetional heat and cool systems, so it will definitely have to be programmed for heat pump set up.
    tnahartley's Avatar
    tnahartley Posts: 2, Reputation: 1
    New Member
     
    #4

    Apr 4, 2012, 07:00 PM
    The Stat was the issue. Had to look up on honeywell's web site. The instructions for programming the unit did not come in the pack. Thanks
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Apr 5, 2012, 03:19 PM
    Hey, thanks for the update. Glad you got it going. Good job, take care.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump blows cool air,then warm air, then cool air again [ 5 Answers ]

My heat pump comes on, blows cool air, then hot air, then back to cool air again. The unit also runs for days at a time without ever shutting off, thus causing my electric meter to be moving very fast, and running up my electric bill. It has been running now for 42 straight hours. What can...

Heat pump heating but no fan blowing warm air on Goodman. [ 4 Answers ]

Heat pump is heating and everything seems to be good except the blower fan is not kicking on in attic to circulate warm air. I replaced the sequencer and the capacitor for the blower. Any ideas, this is on a Goodman. Thanks!

Heat pump not blowing cool air [ 2 Answers ]

Hi, My heat pump has been cooling just great until last evening when the register air was only blowing 62 degrees, even as it cooled outside the register air never dropped down. To be safe I shut it off. Anything I could do other than calling repair? Does refrigerant need to be charged?...


View more questions Search