    Depth of 25 KV cable
    What is the required depth of a 25 KV elect cables
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 20, 2012, 02:34 AM
    Direct buried cables need to be a minimum of 36 inches.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #3

    Mar 20, 2012, 06:26 AM
    TK is correct... but, please also review National Electrical Code
    Article 300 and table 300.50 for any additional requirements you
    May need to consider.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can telephone cable and television cable put in one electrical conduit [ 5 Answers ]

Can telephone cable and television cable put in one electrical conduit?

Connecting VCR, Cable Box, DVD, and Cable Internet [ 2 Answers ]

How do you connect cable wires to the cable box, broadband cable internet, a VCR, and a DVD player and still be able to watch a movie on VCR but also be able to record what's on TV with the VCR.

Need 3" floor depth adjustable cable drain. [ 1 Answers ]

Installing custom shower, need to install cable drain overflow to go through 1 1/2 lite weight concrete, 3/4 plywood, tile and tub liner (membrane). Aprox 3 inch. Who would manufacture this adjustable drain?

Wall mount for cable, how do I prepare for cable line? [ 3 Answers ]

I want to move my T.V. across the room, I have a wall mount with the wire there. What do I do to the wire that is not cable prepared to look like the one that is now being used? I need step by step instructions. If anyone can help me please!! :confused: Signed single mom trying to save a few...

Grounding cable depth when ran underground [ 2 Answers ]

I am upgrading from a 100AMP to 200AMP service. I need to run a grounding wire (bare CU #4AWG) from 2 grounding rods to the main electrical panel: 50 feet. I plan on running it underground. I wonder whether the minimum depth of 24" (18" if in PVC conduit) applies to grounding wire installed...


View more questions Search