    Why does the voltage drop when I turn the motors on.
    Each motor is on a 30 amp breaker subpanel both fed into a 60 amp breaker in the main panel.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 15, 2012, 11:36 AM
    Voltage drop is can be the result of any one or more of several factors.

    Distance of wiring. Either/or utility wiring, feeder wiring, subfeeder wiring.
    Size of wire.
    Loose connections.
    Low voltage from utility.

    Motors draw 6-10 times the running current to start. Long wire and/or small wire, while possibly sized to handle the running current, may be too small or long to handle the high starting current of motors.

    If you get back with more details, perhaps we can work this out.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Voltage drop [ 2 Answers ]

I have to feed a pump it has a load of 30 amps, is 115 volts and is located 1300 feet.

Voltage drop [ 8 Answers ]

How do you compute voltage drop when given a specified distance and cable size?

Voltage drop [ 4 Answers ]

If i have a 3 phase motor running in 440volts and drives the cetrifugal fan, then the voltage drops to 20 percent, what happened to running current does it increas or decrease.

Voltage drop [ 5 Answers ]

I will be running wire to my shop that is aprox 250' from the main elect box at the house. I would like to have 220 volts and 110 volts. The wire will be buried underground the average temp in my area in the summer is 100 degrees. What size wire should I use. I will be welding with a welder that...

Voltage Drop [ 2 Answers ]

I have a 20 amp breaker;there are a total of 7 receptacles on this circuit with a 15 amp GFI on the first receptacle. The first 5 receptacles in line work fine, the last two receptacles which are approximately 70 feet from the 5th receptacle flip the 15 amp GFI off when plugging in a drill. I...