    Breaker to GFCI
    Can a breaker going bad cause GFCI to trip?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Mar 11, 2012, 12:05 PM
    I don't see how. What's the problem?
    yankeet's Avatar
    yankeet Posts: 2, Reputation: 1
    New Member
     
    #3

    Mar 11, 2012, 06:34 PM
    GFI was kicking off, changed it out, no help, finally after trying multiple other things disconnected all but incoming wires, still would not reset! There were a couple times it worked and thought it was fixed but now won't reset at all using either of the GFI's. Have had several instances of other lights in house flickering and one room even staying off then finally coming back on!
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Mar 11, 2012, 10:54 PM
    I would start looking for intermittent open circuits. A GFI outlet will not reset if there is no power or if there is an open neutral. The flickering and other circuits going off sounds intermittent open circuits to me. The first thing I would do is pull a couple outlets and see if the quick connect holes in the back of the outlet was used to wire the outlets. The quick connect method of wiring is notorious for developing bad connections after a period.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I use a 50 amp GFCI breaker to install a pool pump that calls for 20 amp GFCI? [ 5 Answers ]

I am replacing my old pool pump with a variable speed pump that calls for a dedicated 20 amp, 2 pole GFCI breaker, but I have not found an outdoor box with a 20 amp GFCI. The power from the mail panel is coming from a 30 amp breaker and I want to split this line with a GFCI dedicated for the pump....

Circuit breaker trip after install of GFCI breaker [ 3 Answers ]

I'm replacing an outlet under kitchen sink that garbage disposer and dish washer were plugged into because they stopped working. The old outlet was not GFCI. So I'm attempting to replace it with one. Our home was built in the '50s and has no ground line yet. I used an extension cord to plug them...

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

Replacing GFCI Breaker With A Regular Breaker [ 1 Answers ]

I have a 15 amp circuit serving only a single outlet on my deck. It is protected by a GFCI circuit breaker in the home's single 125 amp service panel. I wish to replace the GFCI breaker with a regular 15 amp GE breaker. I will then protect the circuit with a GFCI outlet. I am familiar with...

Gfci breaker [ 2 Answers ]

My question is I have a 50 amp GFCI breaker that I will be installing in the breaker box. I have another 50 amp GFCI breaker box that must be installed within 5 feet away from the hot tub. Is it OK to install both 50 amp GFCI breakers for this hot tub I realize I don't need two GFCI's but I...


View more questions Search