    My brand new hotwater heater keeps releasing 8oz of water from the pressure valve.
    My brand new hotwater heater keeps releasing 8oz of water from the pressure valve. We replaced it but the problem perssists. The warranty company is saying that we need to install a thermal expansion tank for the overflow water. Is this normal? What happens when the expansion tank fills up?
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #2

    Feb 17, 2012, 08:28 AM
    One of the three things are happening:

    1. Pressure valve in bad
    2. You have too much pressure in your plumbing system
    3. Thermal Expansion

    1. We always replace pressure relieve valve with every new heater installation. Did you replace yours ?
    2. Pressure in your house should be set at around 55 psi. Check your pressure. Adjust as necessary
    3. If Thermal expansion occurs, install Thermal Expansion tank

    Back to you. Milo
    Curlyben's Avatar
    Curlyben Posts: 18,514, Reputation: 1860
    BossMan
     
    #3

    Feb 17, 2012, 10:18 AM
    Bump
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Feb 17, 2012, 10:37 AM
    Thermal expansion tank does not fill up with water. Thermal expansion tank is a tank of air. When water is heated it expands, the pressure in the tank goes up and water flows into the expansion tank. When you open a faucet pressure goes down and water flows out of the expansion tank. Generally you only need an expansion tank if you have some device on the cold water line, like a pressure regulating valve, that prevents water from moving back up the cold water line.
    So, yes this is normal and the expansion tank does not fill up. It is maintenance free. Easily installed by any plumber or anyone who can solder pipe, assuming copper pipe.
    taniadkpereira's Avatar
    taniadkpereira Posts: 2, Reputation: 0
    New Member
     
    #5

    Feb 17, 2012, 10:50 AM
    Thank you very much for the information.Very Helpful! Also Thank you for fixing the admin problem I was experiencing.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Loss of hotwater pressure after replacing pipe on electric water heater [ 3 Answers ]

We have an electric water heater. I noticed the incoming water pipe was leaking so my husband replaced it. No more leak. But... now no hot water pressure throughout the house! Please help! Everything was fine before I noticed the small leak and the pipe was replaced!

Problems With T&P valve releasing on hot water heater [ 3 Answers ]

I have a 40 gallon hotpoint gas hot water heater in a foreclosure I bought that set for about a year empty. I had hot water pouring out a line under the house so I capped it (stupid I know). Well after talking to a home inspector he told me that it was probably my pressure relief line and my t and...

Water heater pressure relief valve is releasing water [ 3 Answers ]

It appears my pressure relief valve is leaking as the water is dripping from the pipe outside. There are no other water heater issues. It's a dual valve system. The 125psi is leaking to outside, the 125psi is perfectly dry. People I've called in want to replace the entire water heater which...

Failed t & p valve in hotwater heater [ 2 Answers ]

We have a 4 yr. old gas hot water heater. A few months ago (hot summer) we noticed our therm use was 3x's more for the summer months than last summer. Our plumber determined our t & p valve was not working and he has replaced it. Could you please tell me why a faulty t & p valve caused us to use...

Hot water pressure valve releasing [ 5 Answers ]

My pressure relief valve on the hot water heater is releasing every couple of days. My tank is in an overflow pan. I get about an inch of water in the pan each time. We've replaced the hot water heater. Before that, we replaced the pressure relief valve (twice) on the old water heater. Problem...


View more questions Search