    Access to a Ground Rod
    I am going to do a small slab pour in my backyard, but about 18" from the wall, in the space for the pour is a ground wire. The concrete contractor sugeests that burying the rod in the slab is okay. Does that make sense? Thanks for the help!
    Paul
    [email protected]
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 13, 2012, 12:08 PM
    A grounding electrode cannot be just an 8 foot ground rod buried in the concrete.

    What is allowed, as per the National Electric Code 2008 edition is:

    250.52 Grounding Electrodes.
    (A) Electrodes Permitted for Grounding.


    (3) Concrete-Encased Electrode.
    An electrode encased by at least 50 mm (2 in.) of concrete, located horizontally near the bottom or vertically, and within that portion of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (1⁄2 in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG.

    Reinforcing bars shall be permitted to be bonded together by the
    usual steel tie wires or other effective means.


    You may check with your inspector to see if he would allow an 8 ft rod buried in concrete, but that is not listed above.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Feb 13, 2012, 02:17 PM
    Quote Originally Posted by reg71 View Post
    I am going to do a small slab pour in my backyard, but about 18" from the wall, in the space for the pour is a ground wire. The concrete contractor sugeests that burying the rod in the slab is okay.
    If you are saying that the existing wire to the ground rod is in the way then yes, it is fine to cover it with concrete.
    tommybwiz's Avatar
    tommybwiz Posts: 58, Reputation: 2
    Junior Member
     
    #4

    Feb 13, 2012, 07:06 PM
    We have been allowed (by inspectors and our power companies) to attach the ground wire directly to the rebar in a foundation by means of a ground clamp. This may not pertain to your situation though.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Feb 13, 2012, 08:12 PM
    Quote Originally Posted by tommybwiz View Post
    We have been allowed (by inspectors and our power companies) to attach the ground wire directly to the rebar in a foundation by means of a ground clamp. This may not pertain to your situation though.
    In most all places this is required these days.
    Thing is, that was not even remotely the OP's question.

    reg71, please confirm that you are talking about an existing ground wire and rod.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I ground my generator to a copper rod driven into the ground with coax cable? [ 2 Answers ]

I am going to test my 6000 watt generator. It is recommended that I ground it to a copper rod driven into the ground. I alread have a copper rod that is used to ground my telephone and cable lines. Can I use a length of coax cable to run from my generator ground to the copper rod?

Nec-covering of ground wire from the ground rod to the water pipecables [ 1 Answers ]

I installed a new service meter panel and ground rod. The ground rod is connected to the meter panel via a #4 copper wire to a water pipe located 10 feet away. Is is allowable to bury the #4 wire between the ground rod and water pipe to keep it from being a trip hazard and protect the wire? ...

Ground rod wire is not connected to the ground rod [ 1 Answers ]

My inspection report for a property that I'm looking to purchase said that my " ground rod wire is not connected to the ground rod". I have no idea what something this would cost to fix. He also said that the ground rod clamp was rotten. Am I looking at thousands in repairs?

Ground rod instead of ground wire? [ 7 Answers ]

I'd like to install an RV outlet (120v, 30amp) in our parking area. Unfortunately, I only have two wires available to that location and adding a third wire would be quite difficult. Can I use the two available wires for hot and neutral and drive in a grounding rod next to the outlet for the...

Ground Rod / ground wire [ 9 Answers ]

Hello, I am installing a 100 amp subpanel in my workshop 125' away from my house. I have two ground rods in the ground by the shop, and was wondering if it was necessary to run 4 wires from the house to the shop (two hots, one neutral, one ground), or could I just run the three wires from the...


View more questions Search