    What wire gage
    Running 130 ft to a home hobby shop (1 person). Will be powering a table saw (1hp), drill press (1/2hp), air compressor (1hp), jointer (1hp), miter saw (1/2hp), various hand tools.

    Plan on running single phase but nees to make sure I've got the power and amps to run the equipment w/o ruining them.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 7, 2012, 10:18 AM
    Personally, I would instal direct buried #2 - 4 wire URD cable, which is aluminum.

    Can be sleeve with conduit if soil conditions are rocky.

    #2 Al is good for 90 amps, plus will help with voltage drop for your loads.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #3

    Feb 7, 2012, 10:24 AM
    BikerDuke,
    Are you attempting to keep cost to the minimum or would
    You entertain say... a 60 amp subpanel?
    You could run just one or two receptacles (each on a dedicated circuit) and just swap plugs when you need to.

    If this is a voltage drop question based on the largest load at 120 Volts, it would be the 1 hp compressor.
    At 130 feet and #10 awg wire the voltage drop is about 5%, with #8 the drop is 3%. The electrical code recommends 3% max for branch circuits.

    Be Safe

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can you use 14 gage wire on 20 amp circuit [ 5 Answers ]

Some lights are being feed off 20amp breaker. Can you use 14 gage wire in this circuit to add 3 way switches?

THHN1 8 gage wire for 50 amp circuit. Is this OK? [ 5 Answers ]

I am wiring a hot tub and installed a new 50 amp circuit. I have 6 gage wire (35 feet) from the panel to the outer wall of my house. From there I am preparing to run 95 feet of THHN1 8 gage wire that I will be burying 18" under ground in grey schedule 40 pvc. Two questions. Is 8 gage...

Proper wire gage [ 1 Answers ]

Currently my sub panel in the garage is supplied by 10 gage 2 wire with ground from a 30 amp dbl pull breaker in the house. The run is 30' to the 100 amp box in the garage. The garage is a part time workshop with several power tools on at the same time along with 10 4' fluorescent light fixtures...

12 Gage wire 110 outlet [ 1 Answers ]

What amp breaker should I use for a out side 110 outlet using 12 gage wire.Used for plugging in vacuum cleaner to clean cars.

12 gage wire on a 15 amp switch [ 1 Answers ]

If you can use 15 amp receptacles and switches on a 20 amp circuit, then why won't they accept (quick connect) 12 gage wiring?


View more questions Search