How to wire a thermostat in the aquastat relay type L8148E?
[ 0 Answers ]
I have purchased a Honeywell thermostat RTH2310B1010 and would like to wire it to my honeywell boiler relay L8148E but the wire codes do not match TV W T on the relay and W Y G on the thermostat , what is the procedure to wiring this combination? Thanks!
Installed honeywell L8148E Relay - Copper Coils Burnt.
[ 1 Answers ]
Just had a L8148 installed- Plumber left and 10 minutes later I noticed scent- Took the face plate off- noticed the coils all fried- He is returning this evening- Just curious as to likely issues. Thank you.
Aquastat L8148e.
[ 2 Answers ]
I have a dunkirk boiler pwb-5d , and an aquastat L8148e. The flame rollout sensor grounded out against burner. From a melted wire. In turn caused the switching relay to click on and off rapidly.I fixed the wire on the rollout sensor. Tried to turn on boiler and nothing happened. So I thought the...
Aquastat L8148e dunkirk boiler
[ 1 Answers ]
Dunkirk boiler pwb-5d , and an aquastat l8148e. Replyed After checking to be sure no other control is wired into the aquastat and has failed replace the aquastat contro always double check all circuits Don't know how to reply to the answer so I am doing it like this , So can I safely run the...
Common wire for thermostat and aquastat relay
[ 10 Answers ]
I just purchased a totaltouch P286-1300 which I know is a little bit of over kill for my system, but I like the way it looks. Anyway, I just a simple two wire baseboard gas heating system. When I connect the wires the screen lights up and comes on just fine. When I use the system the thermostat... View more questions Search