    Size of a Junction Box Devices
    I have 5 12-2 wires coming into a junction box, so 11 wires at 2.25 cubic inches equals 24.75 cubic inches. One of those wires is coming from the breaker panel, the others are going out to power switches in 4 other rooms. What I don't know is if I need to add more cubic inches for devices in that junction box because I don't know what is considered a device.
    UsaveU's Avatar
    UsaveU Posts: 25, Reputation: 1
    New Member
     
    #2

    Jan 26, 2012, 05:24 PM
    Ok, I think I found the answer to my question in the NEC.

    A device would be a switch, outlet or light fixture?

    If someone would confirm this for me I would appreciate it.

    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jan 27, 2012, 03:55 AM
    Need to allow two times 2.25 for a switch or receptacle in that box.

    A fixture is not a device, and only needs to be counted if there is a supporting mechanical device inside the box to mount the fixture, which most do not need nowadays.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can a fiber optic cable junction box be used as a pull box [ 1 Answers ]

We have terminated a 24 fiber in a junction (30"x24"x8") and have several 1-2 fiber coming out to various points. The would like to use this box to pull additional multi-fiber through the same box. I believe this is not allowed. I need clarification.

Junction box size [ 5 Answers ]

I am in the process of installing electrical radiant heating under a floor. It's a pretty simple circuit - I have a dedicated 120V 20A circuit connected to a line-voltage, GFI protected thermostat. The thermostat then feeds the radiant mats (there are 6 mats, pulling a total of 13.2A at 120V). ...

Junction box under panel box? [ 1 Answers ]

I am bringing new underground cable into an unfinished garage which is coming directly from the meterbase. The cable will come out of the ground at the garage, run up the outside of the wall for approximately 3 feet (obove the 2 high cinderblocks) and then go through the wall where it will connect...

Number of devices and wires in a box [ 2 Answers ]

I am installing numerous two gang receptacle boxes in a shop/barn area. The boxes are regular metal 4 square outlet boxes connected to 1/2" EMT conduit. There will be six #12awg wires coming in to each box and two duplex receptacles in each box. I will be putting wire nuts on the pigtails, so...

Junction Box size [ 2 Answers ]

I have and oven with 10/3 mc cable attached. I am going to splice this to a 10/3 romex cable that I pulled from the sub panel. Is a metal 3" deep single gang box big enough? How many cubic inches do I need? Thank you


View more questions Search